I have a goodman/janitrol furnace model number gmp075-3. when the t-stat calls for heat the fan turns on and the status light flashes 5 times, which is false flame sensed. i have replace the ignighter and jumped all the the sensors and it still flashes 5 times. any suggestions?

Posted by on

  • corbyware Nov 11, 2008

    Same problem. Any luck? Guess I'm going to replace the control board and see what happens. Changed T-stat and had no luck there. Fans just keep running and running... Oh, SOMETIMES it will ignite but very random.

  • TxJole Nov 13, 2008

    I'm having this problem aswell. First day just the inducer motor would run. I come back today both fans blowing. I stick a volt meter on the ignitor nothing. I close the main blower door it fires up just fine!!!! I pull the main blower door to make sure I got a good seal. Replace it and its back to 5 blinks???? HELP!!!

×

4 Answers

  • Level 1:

    An expert who has achieved level 1.

    Mayor:

    An expert whose answer gotĀ voted for 2 times.

  • Contributor
  • 1 Answer

I Also have the same and other problems with my furnace model # GDS80703AXBB. First the LED kept blinking 4 times and I too jumped the primary limit, that didn't kelp. After several attemps I moved the wires going to the circut board and everything starting working again. After a week It stopped working again, so I pulled the plug out of the circut board checked all wires for for a bad connection plugged it back in. Now the LED blinks 6 times again I move the wires. Then the LED blinks 3 times. Then the transformer burns out. I have burned out 2 transformers and I have ordered a new circut board.

Posted on Nov 15, 2008

  • Level 1:

    An expert who has achieved level 1.

  • Contributor
  • 1 Answer

After fighting this thing for 2 weeks, I changed out the circuit board tonight and I have heat!!!! Barnett Brass is where I got it. $100

Posted on Nov 14, 2008

  • TxJole Nov 14, 2008

    Oh and the new circuit board model # now ends in 13S not 08 like your book says

×

  • Level 1:

    An expert who has achieved level 1.

    Hot-Shot:

    An expert who has answered 20 questions.

    Corporal:

    An expert that hasĀ over 10 points.

    Problem Solver:

    An expert who has answered 5 questions.

  • Contributor
  • 22 Answers

IS it the inducer motor coming on right away, or the blower, becuase if it is the blower than you are out on a high limit, depend on the model goodman puts to manual resets on each side of the blower motor. please give more info

Posted on Oct 28, 2008

  • crazzedrv894 Mar 11, 2011

    I have Goodman GMP075-3 it runs one cycle gas shuts off and house fan remains running. I shut off by opening door and releasing door switch. leave off or twenty minutes close and turn on thermostat and it runs another cycle. look under panel and the led flashes 5 times (false flame sensed) or it starts again, but usually flashes unless left off for same time period.

×

  • Level 1:

    An expert who has achieved level 1.

    Problem Solver:

    An expert who has answered 5 questions.

  • Contributor
  • 7 Answers

Some those codes represent other things as well,,,when u say fan do you mean the combustion fan if so then its not making the switch there is round switch on the side with rubber hose to it,,jumper it if runs try cleaning out the hole on the combustion fan motor,,,if not need to replace the switch assuming the fan is pulling enough vacum,,,not much info to go on,,,need more to diagnose 100% good luck.

Posted on Oct 25, 2008

1 Suggested Answer

6ya6ya
  • 2 Answers

SOURCE: I have freestanding Series 8 dishwasher. Lately during the filling cycle water hammer is occurring. How can this be resolved

Hi,
a 6ya expert can help you resolve that issue over the phone in a minute or two.
best thing about this new service is that you are never placed on hold and get to talk to real repairmen in the US.
the service is completely free and covers almost anything you can think of (from cars to computers, handyman, and even drones).
click here to download the app (for users in the US for now) and get all the help you need.
goodluck!

Posted on Jan 02, 2017

Add Your Answer

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

1 Answer

Goodman furnace a36-20 fan runs non stop


is green wire from thermostat or from outdoor. retrace and change as needed. If not Goodman has a tech support number you can call while looking at unit.

Jun 21, 2014 | Goodman Heating & Cooling

1 Answer

Goodman furnace GMP075-3 The thermostat was in the off position over night and sometime during the night, the induced blower and blower motor came on. The trouble light on board blinks 5 times. I checked...


Need your model # to check the codes but, this coming back on after turning the t-stat off is rare. You may have been in a lockout and the furnace re-started. Some furnaces try to start three times , then lock out. Time out, then re-start. The codes should be on your furnace blower door. Write back with this info and i could help.

Oct 12, 2011 | Goodman GMS90703BXA Heater

1 Answer

I hooked up a coleman electric furnace to a janitrol condenser heat pump . The t-stat wires on electric furnace are red white green and yellow. I added a blue for common off of transformer for digital...


Hi, first of all you need to get a hand full of 5 amp auto type fuses and install one on the hot leg of the 24 volt secondary side of the transformer. Just use 2 female crimp on connectors and put the fuse in the middle of the hot wire. Saves $$$$ on replacing transformers when you have a dead short on the low or high voltage side of any transformer, just a trick of the trade, food for thought. Fuses are much cheaper. On your electric unit, you may not need the common on this to operate the digital stat if it has batteries. This may be your dead short. On the Janitrol condenser, the red is your 24v as you no. They are using blue in place of yellow for cooling. Red is hot, W is heat, G for fan, and blue is cooling on this Janitrol. Keep in mind you are connecting to a heat-pump also, so make sure the wiring is correct. Are you installing this for secondary Heat?? More then likely, the blue common you have added is the dead short as the janitrol uses the blue for a cooling relay in place of yellow. Anyway, use the 5 amp fuse, trick of the trade to save on the transformers. Please keep me posted, as I know know you have this under control.
Shastalaker7
A/C, Heating, & Refrigeration Contractor. Good Luck!

Feb 09, 2011 | Coleman Heating & Cooling

1 Answer

I have outside Goodman-Janitrol furnace and air unit and


two things to try first to get you pointed in the right direction. First disconnect the R or RH wire from the T-Stat. If the furnace turns off (Stops firing w/ fan to turn offabout 90 sec. later) then you more than likely have a bad Thermistat. If it continues to run Pull the R wire from the Furnace circuit board. put door back on furnace if it stops you have a short in the wire. Still Running? Most likely a bad curcuit board. Hope this helps.

Oct 12, 2009 | Goodman GMS90703BXA Heater

1 Answer

GMPN 100-4 furnace. Blower motor runs when not calling for heat.


The board is bad. The unit thinks a flame is present, so it tells the blower to come on. Replace the board.

Oct 07, 2009 | Goodman Heating & Cooling

1 Answer

Goodman furnace


double check your wiring. R terminal on the furnace will provide 24 volts to the t-stat. W terminal in the t-stat will send 24 volts back to the furnace W terminal to turn on the heat. G terminal in the t-stat will send power to the G terminal in the furnace when the t-stat is switched to fan on. Y terminal in the t-stat will send power to the Y terminal in the furnace which in turn will send 24 volts to the A/C outside. The C terminal in the furnace should be connected to the c terminal in the A/C outside as well as to the T-stat. Check the fuse again

Jun 02, 2009 | Goodman GMS90703BXA Heater

1 Answer

We recently bought a new house (to us). It has a Goodman heat pump and Goodman Electric backup furnace(A36-15) with a Janitrol stat. I switched the stat to emrg. Heat when the temp got below...


If you have a volt meter, check to see if you have 24 volts coming from the thermostat on the yellow wire.

If you do, and it is set on emer heat, you have a bad T-stat.


It looks like it is wired properly.

If you have no meter, you could try changing the stat, I reccomend Honeywell or white rodgers.

Let me know if you eliminate the Tstat as the problem and we can go from there.
Chances are its the stat.

Dec 06, 2008 | Heating & Cooling

2 Answers

Janitrol/Goodman GMP075-3 Draft Inducer Fan Won't come on


most forced draft fans are powered by 120 volts . close to the fan is usually a plug that unsnaps. create a call for heat after turning off to clear safetys and see if your getting 120 to fan on initial call for heat. if you are then fan draft motor is bad, usually sold as an entire assembly replace exact as it came out. sequence of operation is..... stat calls for heat via common and white wire to furnace , 24 volts. ......board sences call and sends 120 volts to forced draft ........ motor runs and creates pressure on proofing switch,....... switch closes 24 to board and tells it draft fan is on......... board then energizes ignitor,....... after ignitior glows gas valve is opened and burner lights ........ either ignitor or seperate sensor rod tells board the burner lit........ and a few minutes later the fan comes on and hot air is blown out. if a step is missed or doesn't proof the furnace either trys up to three times to light or locks out. turning off power usually resets safetys and it will resume attempts to lite normally.

Oct 25, 2008 | Heating & Cooling

1 Answer

GOODMAN CMA80905CXBA FURNACE. INDUCTION BLOWER NOT ENERGIZING. GETTING 3 "BLINKS" FROM DIAGNOSTIC LIGHT (LOW PRESSURE SWITCH OPEN). THE A/C WORKS & THE BLOWER FAN COMES ON WHEN THE STAT IS IN...


the pressure switch is closed before the draft motor closes it.the board is telling you that this is not right.pull the wire(either) off of the pressure switch to see if furnace tries to light.if it does,you should replace the pressure switch.

Oct 02, 2008 | Goodman Heating & Cooling

1 Answer

Goodman Furnace m/n GKS90453BKAC


A constant red light (not blinking) indicates that the thermostat is not calling for heat. Of course you know it is but just to be safe, jump out R and W on the board. If it continues to do the same as you indicated, replace the board.

Dec 05, 2007 | Goodman GMS90703BXA Heater

Not finding what you are looking for?
Goodman GMS90703BXA Heater Logo

2,785 people viewed this question

Ask a Question

Usually answered in minutes!

Top Goodman Heating & Cooling Experts

Dan Webster
Dan Webster

Level 3 Expert

8205 Answers

paulcarew

Level 3 Expert

2364 Answers

Brandon Berry
Brandon Berry

Level 2 Expert

407 Answers

Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...