Have gas furnice weatherking model #wgph-10 amer ser#df5d302f349802355 fan won't turn off, heatwon't turn on; checked 24 volt at tstat to green no volts auto 24 -on 110 out of fan concection no 110 out of furn or cool outputs on contol board. tsat all 24 vac ok
    Novelist:
  • 124 Answers
The fan comes on only after the burner fires. so no stat voltage is expected. it is not powering the blower, the elec board is. only after burner lights will fan be energized due to heat build up. usually on older weatherking there is a heat sensor on the bulhead above the burners. it is stuck sounds like to me. try a sharp rap on the right side about four feet up the side and a foot back . if fan stops you know the switch was stuck . probably needs a new fan switch.
Posted on Oct 25, 2008
Frigidaire furnace wont light pilot. we have replaced igniter and pressure switch
Gas valve solenoid have continuity? No continuity replace the valve
Getting 24 volts to the gas valve? No voltage from control board check fuse on control board.
Replace control board.
Any rollout switchs that are open and you won't get 24 volts to the gas valve.
Oct 27, 2011 | Goodman GMS90703BXA Heater
I need a blower assembly for weatherking model#RHCF-100ZK
Go to www.americanhvacparts.com . You can buy bearing and a shaft from any HVAC supply house. They are standard bearings and shaft. Rus
Mar 17, 2010 | Heating & Cooling
I have a weatherking gas furnace that will not blow
Sounds like a bad blower relay. Check the voltage from the board or relay going to the blower for 110 volts. Replace the relay or board if no voltage.
Feb 07, 2010 | Heating & Cooling
Tapan furnice not turning on, The furnice start and the lighter turn on the small fan is running and after about half a minute the first eye turn on for a second and then everything stop
Check to make sure the gas valve is on.
If so it is most likely the heaqt sensor that proves the ignitor is on. Replace the sensor.
Next time post your model number, answer will be more precise.
Oct 10, 2009 | Heating & Cooling
How do I correctly order a new fan control board for my HVAC
You have two wires going outside they should be hooked to Y and C on the control board. If you have a meter check betweenY and C. If you have 24 volts your problem is outside. If your unit has a low pressure control it may be low on gas meaning a leak. Rusty
Jun 03, 2009 | Heating & Cooling
Finding the cooling contactor on weatherking acclaim II gas furna
the "y" terminal sends the hot leg of the 24 volts and the "c" terminal sends the common leg to the condenser..
Nov 15, 2008 | Weather King Heating & Cooling
What part do we replace first?
Door safety switch. You are sure you have power to furnace? jump out the G and R terminals on the furnace control board or turn your thermostat to Fan On to check. Make sure the door safety switch is in the closed position. Fan should come on. No fan, no power to unit. Check Emergency switch, circuit breaker and there may be a fuseable link in the wiring somewhere either above the unit or a condensate safety switch. Get power to the unit. Also check to see if there is a small fuse in the wiring inside the furnace or on the circuit board.