I just flipped thermostat switch to heat and reset the weekly settings, with thermostat on auto, the fan comes on but the furnace doesn't ignite. I checked the furnace ,the light was blinking 3 times.I did a shutdown and startup procedure but still have the same results.
  • subba1980 Dec 05, 2008
    Goodman GMS90904CXA Wont ignite, light blinks 3 times problem, and notify you when a new solution is offered.
  • 1,420 Answers
Ok, you either have a inducer fan issue or a pressure switch issue or a plugged vent pipe. The inducer turns on to establish a draft for the exhaust. If it is not working you will get this error code. If the pressure switch does not sense pressure caused by the inducer, it will give this code. If either the intake pipe or exhaust pipe is blocked (even y just a little) it will give you the same error code. If the condensate hose or receptical is plugged, again it will give you this error code. Good Luck!
Posted on Oct 21, 2008
My good man furnace model gmh80903bnca will not get to temp fan shuts off and burners keep burning then kicks off on high limit then starts process over but never gets to temp set at 655
If you have a switch that can manually turn on the fan, try it to verify the fan works. This is what I think is happening. The normal operation should be thermostat calls for heat, inducer fan comes on, pressure switch closes, igniter glows, main burner ignites and then in 30 or so seconds the fan comes on and stays on until the thermostat is satisfied. Once the thermostat is satisfied the burner shuts off and the fan runs for approx 120 seconds then shuts off. I think the control board that automatically turns your fan on is faulty. On most modern furnaces if the auto fan control fails and the furnace gets to hot and limits, when the limit opens and shuts off the burner it also energizes the fan motor to cool the heat exchanger.
Jan 13, 2018 | Heating & Cooling
Rheem 90 plus classic furnace-Both blowers continue running. Will only turn off when power to furnace is turned off. Thermostat is on Auto. Green light is flashing 3x. Furnace is not heating.
Check your combustion box temp switch. It sounds like it's stuck closed. Fans indoor fan should only come on when the combustion chamber gets up to a certain temp so you're not blowing cold air. With that switch closed, your heater control board is seeing an error
Jan 12, 2018 | Heating & Cooling
Fan will not come on when it's set in auto mode
If your thermostat is being used with an electric heating system and the fan does not start in heating mode on auto; remove the thermostat from the subcase on the wall and check for a switch on the back of the thermostat. A lot of electronic thermostats have a switch on the back that says electric/heat pump and gas/oil. If you have electric heat or heat pump you need to switch it to this side. Usually this is set at the factory for gas/ oil. Gas/oil furnaces have built in means of bringing on the fan and electric/ heat pumps are brought on by the thermostat.
Feb 11, 2015 | Hunter Fan Company 42999B - Heat/Cool...
My furnace works on ac and blows on ac but on heat it does not blow but i hear a humming sound coming from the furnace
Most furnace operating on Oil or gas will heat the combustion chamber before starting fan to prevent cold air draft at start-up, can last a minute or two. Eiter the main flame does not come on or the chamber thermostat have fail. Try to modify fan option on room thermostat from auto to on. Cold air coming out: burner problem or no more oil or gas, warm air: burning chamber thermostat problem, leave room thermostat fan option to on until repair.
Jan 02, 2014 | Comfortmaker Heating & Cooling
Honeywell MagicStat 3200 Fan continues to run--I flipped furnace breaker off for an hour, set stat to off, & flipped breaker back on. fan still runs. Fan control is on Auto.
Hello,If just installed the thermostat check that the wires are not touching anywhere.If not the case you have a open(tripped) HIGH LIMIT at the furnace and the blower will continue to run untill it is reset.
Oct 30, 2010 | Honeywell Programmable Thermostat Heater
Sometimes the furnace doesn't come on when it should
OK so its an all electric furnace no gas? I cant think of anything clicking on an electric furnace except the sequencers or the safety switches.
If this is whats your hearing then the fan should definitely be running.
Feel carefully around the fan motor (I assume this is in a mobile home). See if you detect any heat coming around the blower area close to the fan motor. If so the fan motor may be at fault or one sequencer may be out (the main one of course...) the thing is can you get the fan to come on by turning the auto switch on the thermostat (or if older model the Auto On switch on the furnace) to ON? If so you can "limp by and have heat til someone either checks it or you can go on deeper into it. but to go deeper you'll have to let me know you know where the elements are and that you have a volt meter. and feel comfortable using it especially on HOT wires.
Mar 03, 2009 | Heating & Cooling
Thermostat problems
Have you confirmed that the thermostat is programmed correctly?
Did the thermostat ever control the temperature of the house properly?
When you indicate "kick", are you talking about flipping the Auto-On switch back and forth? The Auto-On switch only controls the fan, and no heating or cooling (Auto - fan runs on call for heat or cool, On- fan runs all the time.).
If "kick" means making the heating work, and if you have the same problem for making the cooling work, chances are good you have bad thermostat.
If the problem only occurs with the heating, and cooling works fine, then the problem could be in the controller board of the furnace, assuming you have a more recent (1990's or newer) furnace.
Jan 16, 2009 | Heating & Cooling
Thermostat seems to be working, furnace does not always turn on
Joss sounds like the anticipator setting on thermostat i would replace it with a digital it will be more actturat . The furnace has to go over temp setting to turn off
Jan 15, 2009 | Honeywell Electronic Programmable...
I had the same problem, I had to remove the lower black rubber stopper right next to the exaust fan and hook up a drain to the unit, as soon as the water drained out the furnace fired right up.