Transfer switch not running "exerciser" program.Clock, exercise program, etc. have be reset.
  • Carl Gehrke
    Carl Gehrke May 11, 2010
    Will the ATS run the "test" feature? If not you may have a broken wire between the generator remote start and the ATS.
    Carl
  • Rick Migliore Sep 04, 2012
    I have a Winco 10K generator.  Runs in manual but will not transfer when power is shut off
4 Suggested Answers
  • 5 Answers
SOURCE: My Kohler 17RES has stopped doing it's scheduled
On your Automatic Transfer Switch ( the little gray box you see on the right in the picture above) you have two blue buttons. One is a Manual test switch. The other has a clock on it and this is your exercise set button. Hold it down for a FULL 3 seconds if you want it to excercise without a load (not powering your home) Hold it down for a FULL 6 seconds if you want it to exercise with a load every week. Your generator will start and run for 20 minutes, and then shut down. Now every week your generator will exercise at the time and day that you pushed the set button.
Posted on Sep 04, 2009
  • 1949 Answers
SOURCE: My generator has stopped exercising, and I also
check battery
Posted on Dec 13, 2010
malarkus
  • 5 Answers
I have a similar model and had the same problem.
If the generator starts when you use the switch located on the generator itself, obviously the battery is fine.
On my model (PSS8000), there are three low-voltage wires that travel from the generator to the transfer switch box: Battery +, Battery - (ground), and "Start". The transfer switch "tells" the generator to start by grounding the "start", i.e. connecting it to Battery -. This is regardless of whether it's the exerciser clock, the manual override toggle switch, or an actual power outage.
In all cases, the control signal goes through that toggle switch -- the one labeled "Start/Disable/Automatic" on the transfer switch. In my case, that switch itself had gone bad. (If you're qualified to do this repair, you'll know how to test the switch with a multimeter.) I was able to find an exact replacement at McMaster-Carr and was back in business in about 10 minutes.
There are two other likely possibilities: That switch on the generator also has "stop" and "automatic" positions. If that switch is faulty, it could be blocking the start signal from the automatic transfer switch. And finally, the wiring between the two could be bad.
When testing, don't forget that while the switch on the generator starts the engine immediately, the switch in the house has a 10-second delay before starting and a 90-120 second delay before turning off.
Posted on Dec 12, 2016
Kohler exercise causes engine spikes and gasping for fuel.
On exercise it isn't under load, you may have too much gas pressure, have the gas pressure and fuel/air ratio checked on the mixer
Dec 16, 2012 | Kohler Generator 20kw 20res W/ 200 Amp...
How do I reset the exercise mode to a new date and time on the Asco 165
Press and hold the exercise button at the day and time you want it to exercise. It will remember this time and will then auto exercise. The ex led blinks and for example 7 times, that means 7 days until ex, then 6 and so on. I hope this helps, emerson power have manuals, or I can send one let me know
Dec 05, 2011 | RTO ASCO 165 Series 200A Automatic...
What is the proper proceidure to set exercise timer on a briggs generator model # 01938 and what year was this model manufactured? thank you
http://www.homegeneratorsystems.com/service_support/manuals/index.cfm?rd=1
This link will take you to their site where you can download their manual.
Setting Exercise Timer
The Home Standby Generator is equipped with an exercise
timer that will start and exercise the system once every
seven days. During this exercise period, the unit runs for
approximately 20 minutes and then shuts down. Electrical
load transfer DOES NOT occur during the exercise cycle
(unless an utility power outage occurs).
A switch on the control panel is labeled “Set Exercise”
(depicted on page 10).The specific day and the specific time
of day this switch is pressed is programmed into the
control board memory.This date and time is then used to
automatically initiate the system exercise cycle.
To perform the Set Exercise procedure:
1. Choose the day and time you want your Home
Standby Generator to exercise.
2. On that day and time, set the AUTO/OFF/MANUAL
switch to OFF.
3. Press and hold down the “Set Exercise” switch for two
seconds.
4. Set the AUTO/OFF/MANUAL switch to AUTO.“Set
Exercise” is complete.
For example, if you press the “Set Exercise” switch on
Sunday morning at 10:00 AM, the unit will run an exercise
cycle the following Sunday at 10:00 AM (+/- 1/2 hour).
NOTE: “Set Exercise” will only work if the unit is in the
Automatic mode and this exact procedure is followed.The
exerciser does not need to be re-set if the 15 Amp fuse is
removed or changed.The exerciser will need to be re-set if
the 12 Volt DC battery is disconnected.
If you want to change the day and time the unit exercises,
simply perform the “Set Exercise” procedure at the exact
weekday and time you want it to take place.
• To prevent possible injury that might be caused by such sudden
starts, always set the AUTO/OFF/MANUAL switch to OFF.
• Remove the 15 Amp fuse before working on or around the
generator or transfer switch.
Nov 12, 2009 | Briggs & Stratton 12,000 Watt Bi Fuel...
My Kohler 17RES has stopped doing it's scheduled weekly exercise. How can I get it exercising again?
Aug 08, 2009 | Kohler 12 kW Emergency Power System -...
Need to reset Timer...need help
Hi Dawn,
I'll ask the obvious question, Does the engine start and run every Thursday at 2:30pm (more or less) or not?
What I see in the field is that people notice the TOD clock on the timer is incorrect due to DST changeover and make a boo-boo while trying to correct it. You seem to have the right idea above so it's better to observe and see if the thing operates like we want rather than fix what might not be broken :-)
Generally speaking...
Generators have 3 switch positions, Off, Auto, and Manual. I think that's the switch on the left side of the panel you mention.
Timers have a Program, Run, and sometimes Override mode of operation. This would be that switch on the right side of the panel above. When in the "Run" mode almost all timers display the current Time Of Day somewhere, many blink the colons in the display to indicate that something is happening.
Let me know if you need further help,
Carl
Mar 19, 2009 | Winco 200-Amp Automatic Transfer Switch -...
Gen. set won't auto start.
This sounds a little like a bad wiring problem between the transfer switch and the generator. But before I leap to any unfounded conclusions let's make sure I understand just which Guardian generator and transfer switch you have. The generator I think you have is an air conditioner sized box that has a 2 cyl air cooled Generac GT990 engine in it. The control panel has a 15 amp fuse, and maybe a 7 amp one, some LED indicators, a 3 position rocker switch (manual,off,auto), and a momentary set exercise switch. If you look inside your transfer switch there is the transfer mechanism, a single relay, either 2 or 4 fuses, and a terminal board where 4 small control wires connect to the generator. The control wires will be labeled N1, N2, 193, and 23.
If all of that is true then I'll also assume that the generator is blinking all of the LEDs and as soon as you put the rocker switch in the manual position the generator starts and the transfer switch moves to the "generator" position. It shouldn't do that, manual means switch the switch manually too. :-)
Let's take care of the exercise setting first. Switch the main output breaker of the generator to the "off" position, this prevents the transfer switch from activating even if the generator runs. Next put the generators rocker switch into the "Auto" position and wait at least 1 minute, if the generator starts we have to fix the wiring between the N1 and N2 terminals in the transfer switch and the matching terminals in the generator before we can proceede. If luck was with us and the generator is just blinking its LEDs at you, press and hold the set exercise switch for 30 seconds, you're reseting a "watchdog" type circut so it has to be for the whole 30 seconds. When you let go of the set exercise switch the LEDs should blink another 10 times or so, then the generator should start and run its exercise for 12 minutes more or less and then it'll shut down. At that time the only LED that should be lit is the green "system ready" one and it should be steadily lit. Remember to close the output breaker again.
Next let's address the transfer switch issue. If I've understood you correctly, the transfer switch moves anytime you turn the generator on. The only reason a regular old RTS type transfer switch could do this is that it's being commanded to transfer. It works like this, the 2 coils that move the transfer mechanism get powered by the source we're trying to switch to, once the switch gets into the position it's going a pair of limit switches disconnect it from the power supply so that the coil is only "live" during a transition. Spring loaded contacts hold the switch in either position once it's more than halfway towards either one. The relay inside the box is also in line with the limit switches so that if the relay is deenergised the switch will try to get to the utility position and stay there, it can't if there is no utility power to drive the transfer coil. On the other hand if the relay is energised, the switch will try to get to the generator position and stay there, if there is no power from the generator it can't because the generator is what drives that bottom transfer coil. So I think that for whatever reason the relay in your transfer switch is staying energized when we don't want it to be.
On the terminal board inside the transfer switch you should see terminals labeled 194 and 23, these are the power to the relay coil (194), and the ground to transfer signal (23). With the generator set to off, and a fairly quiet room, disconnect the wire from terminal 23, if you can hear the relay coil click on and off when you touch the wire to terminal 23 there is something wrong with the wiring at the generator end of things. You should also see 12 volts DC between terminal 194 and ground, this comes from the generator too.
If the relay didn't click back and forth above check it by using a short piece of wire to connect terminal 23 to ground, if the relay isn't energised when terminal 23 is grounded and deenergized when terminal 23 is open you either have a bad relay or a problem in the grounding of your system. To get a bad relay fixed for free call up Guardian, register the generator (you'll need proof of purchase), and get them to tell you where your nearest warrenty service person is. If you tell him about this post he'll bring a relay with him when he comes to you.
If you're satisfied that the relay in the switch is working properly, we're on the trail of a wiring problem at the generator end of things. If the generator has just been installed you should carefully check that wire 23 hasn't been connected to terminal 0 at the generator terminal block. It's easy to get this connection wrong when doing th e install. The other thing that can go wrong is that the wire can get pinched inside the conduit and short to ground. To check this disconnect both ends of wire 23 and measure between either one and ground, you should get nearly infinite resistance.
If you've proved to yourself that all of the wiring is correct, and the generator is properly grounded, you probably have a broken control board in the generator. To get the control board replaced use the same procedure as the relay above.
If that doesn't get this resolved for you post a comment and we'll try a different approach.
Regards,
Carl
Mar 05, 2009 | Generac Guardian 200 Amp Transfer Switch...
Winco 200-Amp Automatic Transfer Switch - 4WATS200-31R Logo
105 people viewed this question
Top Winco Electrical Supplies Experts
John Trevino
J.D. Browning
J.D. Browning
Tom Chichester
Are you a Winco Electrical Supply Expert? Answer questions, earn points and help others