Question about Dryers
Drawing combustion air for a gas dryer
Can you tell me where the combustion air is drawn from? I have a laundry room within a bedroom and was told by the fire inspector I could not draw the air from a living space. I want to know if I can buy or fabricate a duct to draw air from an alternative area such as the attic. He told me I caould have the dryer there if I can could draw the air from the attic.
  • Anonymous Oct 07, 2008
    nnnnnnnnnnn
I am assuming that this is a gas dryer not an electric dryer.
Per the 2009 Uniform Mechanical Code Section 902.0
(B) Gas utilization appliances shall not be installed so its combustion, ventilation, and dilution air are obtained only from a bedroom or bathroom unless the bedroom or bathroom has the required volume in accordance with Section 701.2. [NFPA 54:10.1.2]
Section 701.2 basically says you need to provide adequate combustion air. One way is if the volume of the space is 50 cubic feet per 1000 btu. I personally think it is a bad idea to obtain combustion air from a bedroom even if it has adequate volume; it used to be prohibited by the Uniform Mechanical Code. The combustion air requirements are based on the BTUs of the appliance not the CFM. For gas pipe sizing purposes the Uniform Plumbing Code says that clothes dryers have a BTU input rating of approx. 35,000 BTUs. One 4" duct to the attic with the opening of the duct inside the closet within 12 inches of the ceiling would provide enough combustion air per the "One Permanent Opening Method" in UMC chapter 7.
Make up air is a different requirement than combustion air. Chapter 5 of the UMC states that if you have a dryer in a closet you need to provide a make-up air opening of 100 sq inches. The make -up air is to replace the air that is being exhausted not to provide air for combustion. The make -up air could be taken form the exterior of the building or another room within the building. Technically the closet should be insulated and weatherstripped if you get the make-up air and combustion air form the exterior.
Sorry doc john but the fire inspector is not talking about the exhaust duct (environmental air duct). That is required no matter where you have installed the dryer and is a totally separate
Posted on Oct 05, 2010
The inspector is correct about the make-up air or combustion air. Most appliances, and definitely fuel burning appliances, require fresh air to offset the discharged air that comes, in your case, from the clothes dryer exhaust (where the lint discharges).
THat air needs to come from either a room that is not a bedroom or bathroom or from the outside or from a combination of both. The room for the combustion air needs to be 50 cubic feet per 1000 btu of aggregate input air.
The easier way is to often have a duct to the outside. A typical gas dryer requires 150 CFM of combustion air, which you can achieve through a 6" round pipe.
Posted on Nov 25, 2008
  • 943 Answers
HI, thanks for the question. you are not drawing air, with the vent from the dryer. you are blowing air to the outside. and cannot be vented to the attic. must go to the outside . thanks the appliance doc.please rate my answer.
Posted on Oct 07, 2008
I have a 50 gallon rheem direct vent natural gas heater. The pilot light goes out on an infrequent but aggravating basis. I replaced the thermocouple one time and it got better for about a year but has...
Open following links for pilot light help:
http://waterheatertimer.org/How-to-install-gas-water-heater.html#troubleshoot
http://waterheatertimer.org/pdf/Pilot-light-will-not-stay-lit.pdf
http://waterheatertimer.org/images/Negative-pressure.jpg
http://waterheatertimer.org/pdf/Bosch_Ventilating_tight_houses.pdf
Since pilot light goes out and can be re-lit, problem is probably not thermocouple, gas control valve, or air in gas line. But these things can factor in as contributing factors.
Problem is likely one of following or combination of following including dirty burner parts, tight house, incorrect vent lengths, negative pressure caused by other venting appliances, condensation dripping down into combustion area, and inadequate oxygen supply due to hot or closed-off room or attic location.
Gas water heaters draw air from surrounding area. If water heater is located inside house, then air has to enter home through cracks and when doors and windows are opened. Other gas appliances and vent fans also draw air from same indoor area. When other vent fans turn on, air can be drawn down the water heater vent and blow out pilot light.
Inspect combustion chamber to make sure there is no condensate water dripping down from incorrect vent that is putting out flame. If combustion chamber is dry, then close doors and windows. Turn on all vent fans and gas appliances that vent outdoors, and see if water heater pilot goes out.
Consult with plumber or product manual about proper horizontal and vertical lengths of vent pipe for your model. Have plumber clean combustion parts and inspect vent termination and check gas pressure and bleed gas line.
Add louver opening to outdoors so air can enter room where water heater is located.
Aug 05, 2011 | Rheem 50 Gallon FVR NATGAS Water Heater...
I have an LG Neo Plasma air conditioning unit in the living room and the Inverter in the bedroom. I understand these are set up to work together, however, the bedroom unit starts to freeze up (ice)...
I assume its the outside unit of the bedroom that freezes up ?? If the outdoor temperature is below 5 degrees celcuis, its likely to freeze up on the outdoor coil ( On heating mode), there is a defrost function which defrosts the machine automatically. If the indoor unit starts to freeze up ( on cooling mode), I would suggest that there is a shortage of refrigerant gas. Especially if the indoor unit starts to "spit" water out when it is running. There may be a gas leak due to a pipe failure or loose flared fitting. These must be rectified before recharging with gas.
Aug 04, 2011 | Heating & Cooling
CO too high brand new kane 425 on a brand new condensing burner
Only a few things can cause high CO, too much combustion air, too little combustion air, wrong gas pressure or wrong type of gas (LP or Naural) or exhaust being drawn into combustion air and reburned (contaminated).
Feb 21, 2011 | Heating & Cooling
I have 2goodmanGKS9 gas furnaces(propane) installed on 27 Dec 2009. Both units are working. One is in the basement adjacent to the rear outside wall. Lower unit heats about 1200 square feet. Lower...
well lets start with the 2" pvc pipe. that is a combustion air intake it does not put air into the room, i hope. this is a 90% furnace and they should have installed it that way. there should be 2 pipes to the outside the other is combustion gases. the dust problem maybe caused by the air return pulling the air to that room. the bedroom normaly does not get the trafic that the rest of the condo does.so it would not have as much dust.
Feb 10, 2011 | Goodman Heating & Cooling
There is black "dust"all over
the dv 215 uses no room air for the combustion. it is called a sealed combustion unit all combustion air and vent gases are outside of the building. look at the vent cap outside. is it black? if not unit is most likely working ok. if it is black you need to have it checked. so unless the unit has been damaged you should be getting no air from the combustion into your room.
Feb 08, 2011 | Empire DV-215 Direct Vent Natural Gas...
How much ventilation is needed for operation in 250 sq ft room?
A lot of variables in the question you asked. First, you need to convert your square footage to cubic footage. To do that multiply your square footage by your ceiling height. Assuming you have the standard 8' ceilings, your cubic footage is 2000 cubic feet. Also, what is the maximum BTU Output of your heater. Will the heater be the only heat source?
Now, how air tight is this room: fair, average, excellent? Also, is there a door opening(s) to the rest of the interior of the house? Will the door(s) remain opening during times the heater is in operation? Is this room, a bedroom? If it is a bedroom, the maximum BTU Output can not exceed 10,000 BTU's.
If it's not a bedroom and the maximum BTU Output range does not exceed 20,000 BTU's, you should be fine, as long as this room opens into the rest of the house and the door is left open. Higher than 20,000 BTU's will cause a problem.
Keep in mind, these vent-free heaters use interior air for combustion and as far as BTU Output is concerned, more is not better. Because, you are capturing all the heat. Safe placement of the heater is very important. Always keep combustible items at least 3' from the front of the heater. And never near draperies. The back of the heater should be a minimum of 12" off the wall.
Vent-free gas appliances are very safe when used as the manufacturer intended/specified. However, they are not maintenance free and should be cleaned and serviced at least once a year. Not only to maintain proper operation and efficiency, but equally as important SAFETY.
Feb 01, 2011 | Dyna-Glo Double Tag-a-long Heater
Can combustion air come from bathrooms or bedrooms
Yes it can come from any room. Just remember that the air coming in has to go out of the room just as well.
Sep 30, 2010 | Dryers
Dryer does not dry
hi,
need to know if its gas or electric, easy way to tell is to look at the power cord going into the dryer, does it plug in next to the washer or does it have a thicker heavier plug near the floor? thicker plug means its electric, smaller cord means gas. Dryers are dangerous appliances. If you have any doubt what yoru doing stop and write here or call a pro. Be careful to shut the breaker off in the fuse box or shut the gas off outside the house before you do anything else. Most likely if its electric the element burnt and you need a new assembly, or if its gas has their been a disruption of gas service lately? How ******* is your laundry room? You should always leave the door open to your laundry room so the dryer can breathe. If you come to find that your laundry room may not have enough airflow, the thermocouple in a gas dryer will go if it cant breathe also. let us know
hope that helps
Jul 10, 2008 | Whirlpool Dryers
Smell Gas.
you need to clean out you venting ...it is most likely clogged or filling up
Jan 02, 2008 | Maytag MDG2706A Gas Dryer
Dryers Logo
2,554 people viewed this question
Top Dryers Experts