SOURCE: I want to adjust the
To enter the adjustment mode, press the UP, DOWN, and I buttons simultaneously for three seconds. Press the I button until the feature requiring adjustment is displayed:
• HL —High Limit.
• LL— Low Limit.
• Ldf —Low Limit differential.
Then press the UP and/or DOWN buttons to move the set point to
the desired value. After 60 seconds without any button inputs, the
control will automatically return to the READ mode.
(copied from honeywell's instructions)
to clarify the differential is cut in minus the cut out.
Hope i can be some help to you.
Posted on Apr 21, 2008
  • 19396 Answers
SOURCE: I have installed honeywell aquastat
If aquastat wirings are ok, and control module had been set up properly, the the furnace should start.
Check if bypassing the control the furnace starts, if it starts then check aquastat wirings.
If it depends on the furnace, check the valve, the safety sensor and the ignitor.
Here is the guide to set up the Aquastat control:
Guide to Setting & Wiring Heating System Boiler Aquastat Controls
Posted on Sep 13, 2008
  • 1952 Answers
it ll operate only wen it gets fault current in main supply..can u tell how come u know tat it is workin?
  • 234 Answers
SOURCE: what would the correct high and lo and diff
I would say high if you need cooling. If the tempature is cool enough for you then set it to low.If you are hot and need more cooling then high.
Posted on Apr 07, 2009
  • 119 Answers
SOURCE: I had a Honeywell Thermostat
Is this a new hvac system? A new furnace can work differently than your old one. Does it shut off after a minute or two or continue to run? If it continues to run then call that professional back and let him fix it. If it shuts down after a minute or two then it is a feature of the new thermostat to squeeze all of the cool it can from the a/c coil and ductwork.Some of them have settings that you can adjust for blower delay on and off, read the manual that came with the t-stat and see if it does.
Posted on Jun 17, 2011
I have a Honeywell aquastat that was set at 160 on the high and 170 on the low I believe the circulator is locked out how can I manually reset that
Something is backwards here. Typically, HIGH limit should be 180 LOW limit 160 with 10-15 degree differential, depending on boiler size, load, etc. If it is digital and you don't have the instructions go to link below. If its the old dial type you should see 3 dials. one labeled HI, one LOW and one DIFF.
Nov 08, 2017 | Honeywell Heating & Cooling
I have installed honeywell aquastat relay per instruction manual on my dunkirk xeb-4 lp boiler furance with honeywwell ignition unit s8610u but it wont ever start the exhaust fan checked everything several...
Sep 13, 2008 | Honeywell Heating & Cooling
Why when my siemens RDJ10RF room thermostat has the arrow asking for heat does my boiler not fire up so i don't get any heating.The water heats up ok though?
You have a triple aquastat that maintains a temperature level needed to provide hot water. but you are not getting the thermostat to operate the central heating. The thermostat is a switch that operates by temperature. if you have tried raising the thermostat and the system did nor kick in try jumping the thermostat terminals in the aquastat . if that works then the problem is either in the thermostat or the wiring to the thermostat. also with a electrical tester." while the thermostat is jumped" test the c1 and c2 terminals to see if power is going to the circulator. If not then you need a new aquastat. if you have power and the pump is not moving water replace it.
Oct 11, 2014 | Water Heaters
Wickes 102 combi boiler constantly loosing water pressure
It sounds like your thermostat could be the problem. Have you noticed the boiler cutting off at all, or does it run continuously until it goes out on low water?
You stated, "when boiler is on", so I am wondering how you get the boiler on. If your boiler is controlled by a thermostat, you need to check it for a cold draft possibly from behind the thermostat in the wall where the wires come through. The thermostat should never be on an outside wall. The thermostat could be defective.
An aquastat can also control your boiler. If you have an aquastat, check the setting, typically 175 - 180 degrees. You should also have a "high limit" which should be set at 210 - 220. Some people run that high side limit higher; not a good idea - defeats the purpose. If the aquastat is set too high, the boiler will operate too hot and the problem you have will occur.
"pressure rises and pressure relief valve opens" This could mean that your pressure switch is prematurely venting. Check boiler temperature to see exactly at what temperature the T&P valve purges. If it blows off below the high side setting, either adjust or replace. The T&P valves are usually not adjustable. That blow off temperature is stamped on the head of the valve. So, if it discharges too soon, replace it.
Have you actually seen evidence thgat the T&P valve is opening? You may have a bad bladder in your expansion tank and your system may have air in it. Your boiler should have 12 psi when cold and 20 - 22 psi when operating. Check your boiler pressure guage.
this eventually drops below the minimum operating pressure" Technically, there is set point for a NO MINIMUM OPERATING PRESSURE. That is a function of the amount of water in the boiler. If the T&P is blowing off, it will vent water from the boiler and the boiler pressure will go down. There is a minimum operating TEMPERATURE.
Your boiler could be low on water. You will have to manually fill the boiler. Be careful of thermal shock to the boiler. Feel the piping, and fill only when the circulator is running. Make sure the water is not going directly into the boiler. The supply water should go into the circulating supply side which feeds the radiators, radiant floor, or base board circuits.
All this will adversely affect your hot water. The heat exchanger for the potable hot water may have scale build up in it. Using the hot water keeps the boiler running, and a scaled heat exchanger will give you cooler hot water and the boiler keeps running. If this is a problem, you will need to replace the heat exchanger. A better idea is to not use the boiler for your domestic hot water. Why run the boiler in the summer?
Feb 02, 2013 | Water Heaters
Does the boiler thermostat control the heat of the radiators as well as the hot water temperature? Does the thermostat control the water temperature and the pump - as our pump seems to be on all the...
There should be a control called an aquastat that regulates the temperature of the boiler. The thermostat will turn on the circulator to start the flow of water through the radiators. If the water coming back from the radiators is very cold, a control will shut off the circulator until the boiler can come up to a predetermined temperature then start the flow of water again. If you have a tankless coil for domestic hot water, you now have a triple aquastat that maintains the temperature for domestic as well as the boiler temp. So yes the boiler thermostat (aquastat) does control the heat of the radiators and domestic hot water. No the pump is regulated by your house thermostat. You should take an amp draw on the boiler and componants to find out what is drawing more electricity than it should and popping your fuse.
Feb 19, 2011 | Heating & Cooling
Looking for simple wiring diagram to wire ******** aquastat
What are you fanning??? the fire?
Do you have a circulator that circulates when the water is up? Many controls have a AUX connection ... wire the AUX to your fan --- alaternatively, wire directly fron your circulator connection to the fan.
I hope I understood your question ...
Let me know what happens.
Oct 16, 2009 | Honeywell International Honeywell&...
I want to increase the boiler temp by using the your aquastat
Warning! Can cause electrical shock! Here is the instruction manual
for L7248c
Jan 12, 2009 | Water Heaters
Boiler will not shut off
boiler does not shut off when thermostat reaches temp, i already replaced aquastat but condition still exists
Nov 14, 2007 | Heating & Cooling