Question about Goodman CLQ36AR49 Air Conditioner
Re-located condenser, trying to charge unit in cold weather. How do I do this?
    Problem Solver:
  • 6 Answers
It's probably too late to recommend capturing (bottling) the charge in the condensing unit...... With that said the absolute 100% way to charge any unit is to use the weight method. If you look on the nameplate of the unit it will provide you the amount of refrigerant needed in lbs and ounces, the manufacture instruction manual will give you the additional weight needed for the lenght of the line set. In the event you don't have the ability to weigh the refrigerant accurately you can always wrap the condensing unit with a blanket reduce the condensing capacity of the condenser this will simulate a warmer ambient and allow you to charge the unit. If the unit has a fixed orfice metering device you can use the superheat method, if the unit has a TXV (thermal expansioin valve) you should use the subcooling method. Either of these methods with detailed proceedures can be found on any of the popular search engines. Hope this helps and good luck!
Posted on Oct 05, 2008
What makes the condenser fan shut off but the compressor keeps running but not every time
Condenser fans cycle on and off to control the temperature/pressure of the refrigerant in the condenser. This is normal operation.
As to cooler weather start up and tripping the breaker; how cold is it when you are running it? If it is too cold you could be pumping liquid refrigerant back to the compressor, slugging it and causing it to trip a breaker. However, many things can cause an air conditioner to over-amp and trip a breaker but this tends to be more problematic as the weather is hotter.
Feb 20, 2015 | Heating & Cooling
Heat pump condenser fan starts then stops in cold weather
does it heat ok? this is normal in cold temp as fam is not needed in cold temps. try it on warmer day and it will probably run. dont think you have a problem
Jan 30, 2014 | Heating & Cooling
The condensing unit is more than 75 feet from the evaperator. In the very hot weather the unit will not cool. Is there a line size increase recommended for this distance?
No. 75' of distance between condenser coil and evaporator coil is not considered abnormal at all. I would look elsewhere for reasons your unit does not cool in very hot weather, i.e., dirty condenser, low charge, improper sizing of AC and cooling space to name just a few.
Jun 10, 2011 | Heating & Cooling
Want prices on outside unit fan condenser
When I am called to replace a outdoor fan motor I charge $330.I am in las vegas and the charge varies form company to company.The fan motor itself is approx $80 my cost(230v 1 phase condenser fan motor).
Jul 21, 2009 | Weather King 10AJA3001AH Air Conditioner
Compressor freezes up at night and some during day.
You are being ripped off. The ambient (outdoor) temperature at night is low and therefore proper condensing does not take place causing the refrigerant to pool in the condenser and starving the evaporator. This causes a lower temperature in the evaporator resulting in "freeze up" which is often mistaken for a loss of refrigerant.
The proper thing to be done is to block off the condenser air causing the high side pressure to rise until the eqivillant of 110*F condensing temperature.
You can also install a low ambient kit which will cycle the compressor off when the temperatures fall
Jun 07, 2009 | Weather King 12AJA4801AH Air Conditioner
Charging a central air conditioner in the cold weather
The copper tubing has cracked and water has leaked onto my roof. I have shut off the water valve that runs to the aircodtioner but cannot get someone over until the morning. It is a cold night. Will this be sufficient until I can get someone over in the morning. It's not that cold but there is a possible storm coming thru.
Oct 05, 2008 | Goodman CLQ36AR49 Air Conditioner
DE500P Dehumidifier: Does not dehumidify even though set to dehumidify. Fan will turn on when RH above setting, and stay on, since humidity doesn't drop. Filter is clean & pail empty.
Locate and touch the cooils located, usually, above the condensate collection pan, ("pail empty"). If the coils are not cold, or cool to the touch, the unit has lost its charge of refrigerant. This would explain why the unit fan is working, but there is no condensate, as there is no coolant (charge) to cool the coils and "pull" the hunidityout of the air.
Jul 07, 2008 | DeLonghi Heating & Cooling
Not cooling predictably
Possible causes are dirty filters, dirty condenser coil, dirty evaporator coil, or low referigerant charge. Any one of the conditions will affect heat transfer.
Check the filters in your indoor unit, If they seem to be clean and replaced on a regular basis, your evaporator coil is probably in good shape. Unfortunatley on some Weather King models even checking the evaporator coil is not possible due to the extensive amount of referigerent lines that block access to the coil without some major work including evacuating the refrigerant.
The most likely cause is a dirty outdoor condenser coil. On weather king models you will have to remove the casing that surrounds the coil because is is built in such a way that the condenser coil cannot be properly cleaned with the casing in place. Once it is removed make sure breaker is switched off and clean the coil with a water hose.
If your outdoor coil is not dirty then it is a refrigerent problem.
Jun 10, 2008 | Weather King 10AJA3601AH Air Conditioner
Goodman CLQ36AR49 Air Conditioner Logo
42 people viewed this question
Top Goodman Heating & Cooling Experts
Dan Webster
Dan Webster
paulcarew
Brandon Berry
Brandon Berry
Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others