Question about Goodman CLQ36AR49 Air Conditioner
Charging a central air conditioner in the cold weather
Re-located condenser, having trouble charging unit the cold weather
The copper tubing has cracked and water has leaked onto my roof. I have shut off the water valve that runs to the aircodtioner but cannot get someone over until the morning. It is a cold night. Will this be sufficient until I can get someone over in the morning. It's not that cold but there is a possible storm coming thru.
Posted on Oct 14, 2008
R-22 home condenser unit low side and high side pressures when running
Pressures look good but to know if it is charged correctly you have to do a sub cool or superheat to know for sure. Rule of thumb is if turn unit it on let it run 10 minutes. If the suction line sweats and is cold. Might be proper charge.
Jun 24, 2014 | Ruud Central System Air Conditioner
Outside central air conditioning unit not working, is there a reset button?
Hello my name is Heath it will be my pleasure to assist you. The first thing to check is the filter in the furnace or air handler. Also check the inside coil to be sure its not frozen up. Does the air coming out feel cold? It sounds like the unit could be low on charge which means it has a leak and should be leak checked repaired and properly charged. You would need refrigeration gauges to put on the system in order to properly check the refrigerant charge in the system. One other thing could be a dirty condenser coil. Turn the power off to the unit and use a garden hose with a strong nozzle and spray water through the whole coil to try and blow any dirt or debris through the condenser coil in the outside unit.
Sep 05, 2011 | Haier ESA3125 Wall/Window Air Conditioner
I have a central air unit that the line has frozen. How do i fix this?
Shut it down and keep the fan on so it will thaw out...then check the filter and have someone check the freon charge...
Here is a tip about troubleshooting your air conditioner...
There are many things that can cause your air conditioner not to cool…
Air Conditioner Trouble -Review the Possibilities
http://www.fixya.com/support/r3571569-air_conditioner_trouble_review_the_possi
heatman101
Aug 21, 2010 | Weather King 12AJA4801AH Air Conditioner
Central air system blows cool air not cold and
your indoor unit is only circulating the air in the house. for your condensing unit. check your breaker in the electric panel. your contactor or your capacitor.
Aug 09, 2009 | Carrier Heating & Cooling
Compressor freezes up at night and some during day.
You are being ripped off. The ambient (outdoor) temperature at night is low and therefore proper condensing does not take place causing the refrigerant to pool in the condenser and starving the evaporator. This causes a lower temperature in the evaporator resulting in "freeze up" which is often mistaken for a loss of refrigerant.
The proper thing to be done is to block off the condenser air causing the high side pressure to rise until the eqivillant of 110*F condensing temperature.
You can also install a low ambient kit which will cycle the compressor off when the temperatures fall
Jun 07, 2009 | Weather King 12AJA4801AH Air Conditioner
Re-located condenser, trying to charge unit in cold weather. How do I do this?
It's probably too late to recommend capturing (bottling) the charge in the condensing unit...... With that said the absolute 100% way to charge any unit is to use the weight method. If you look on the nameplate of the unit it will provide you the amount of refrigerant needed in lbs and ounces, the manufacture instruction manual will give you the additional weight needed for the lenght of the line set. In the event you don't have the ability to weigh the refrigerant accurately you can always wrap the condensing unit with a blanket reduce the condensing capacity of the condenser this will simulate a warmer ambient and allow you to charge the unit. If the unit has a fixed orfice metering device you can use the superheat method, if the unit has a TXV (thermal expansioin valve) you should use the subcooling method. Either of these methods with detailed proceedures can be found on any of the popular search engines. Hope this helps and good luck!
Oct 05, 2008 | Goodman CLQ36AR49 Air Conditioner
Not cooling predictably
Possible causes are dirty filters, dirty condenser coil, dirty evaporator coil, or low referigerant charge. Any one of the conditions will affect heat transfer.
Check the filters in your indoor unit, If they seem to be clean and replaced on a regular basis, your evaporator coil is probably in good shape. Unfortunatley on some Weather King models even checking the evaporator coil is not possible due to the extensive amount of referigerent lines that block access to the coil without some major work including evacuating the refrigerant.
The most likely cause is a dirty outdoor condenser coil. On weather king models you will have to remove the casing that surrounds the coil because is is built in such a way that the condenser coil cannot be properly cleaned with the casing in place. Once it is removed make sure breaker is switched off and clean the coil with a water hose.
If your outdoor coil is not dirty then it is a refrigerent problem.
Jun 10, 2008 | Weather King 10AJA3601AH Air Conditioner
No cold air
Freezes up is only caused by either low on freon or low aiflow across the indoor coil, which could be caused by dirty or blocked filter ,,dirty fan blower wheel or pluged coil.
May 27, 2008 | Weather King 10AJA6001AH Air Conditioner
Goodman CLQ36AR49 Air Conditioner Logo
197 people viewed this question
Top Goodman Heating & Cooling Experts
Dan Webster
Dan Webster
Paul Carew
Tim Whalen
Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others