Question about Goodman GMS90703BXA Heater
My goodman gmt090-4 shuts off about 10 sec. after burners ignite
The venter blower, igniter, gas, flame all go on as they should. Then about 5 sec. after the igniter turns off the gas shuts off. I changed the flame sensor thinking that was the problem, but still the same. Any advice welcomed
  • 1 more comment
  • Anonymous Oct 17, 2008
    having the same problem with goodman gmp-075-3
  • rbrown923 Oct 19, 2008
    I have GMT 70 and the gas shuts off after about 3 minutes of running then `1 minute later it recycles
  • mikem1204 Oct 20, 2008
    I have a GMP 075-3 with the same problem. Unit will cycle on for about 1 few seconds, then turn off, and cycle back on for a few seconds. This repeates for about 5 minutes, then stays off for about 10 minutes and starts back all over. Have not changed out any parts yet, so the wire should still be connected.
Clean the sensor with a piece of fine sand paper. It gets a coating on it after a few years of service. I had my cleaned for $160, it took five minutes.
Posted on Feb 03, 2009
Check the pressure sensor. I tapped on mine a few times, removed the hose and checked it for blockage and replaced. It has been working fine since. I do have a new sensor on order.
Posted on Oct 22, 2008
Make sure you trace the wire to the flame sensor back to the board and see that it is still connected.
Posted on Oct 11, 2008
Goodman furnace has 3 blinking lights, indicating pressure switch stuck open. Any help?
The flame sensor needs to be cleaned. This video might help you understand how to clean the flame sensor.
Oct 05, 2012 | Goodman Manufacturing Goodman GMH950704CX...
I installed a new goodman unit this past spring. It seems to work ok to good in the day time but the tempature is warmer so we do not need as much heat. At night I know the thermostat is coming on. I...
Heating Mode (Goodman Service Manual)
· The furnace control checks for an open main limit (this
limit is normally closed). If the limit is open, the furnace
will remain inoperable until the limit is closed. During
an open limit the circulating air blower will be
energized. The status light will blink four (4) times.
· The room thermostat reacts to a demand for heat.
· The control will then check to insure that the vent
pressure switch is open. If, at this point, the vent
pressure switch is closed the control will blink two (2)
times and will remain inoperable until this situation is
corrected.
· The venter blower is energized.· The vent pressure switch will close when it detects a
pressure in excess of its setting. If the pressure switch
fails to close the status light will flash three (3) times.
The sequence cannot continue until the pressure switch
closes.
· After a pre-purge of about ten (10) seconds the electronic
ignition device will be energized.
· After a slight delay the gas valve will open.
· The burners will ignite and the flame sensor will detect
the presence of flame. The ignition device will
deenergize. If the sensor does not detect the burner
flame, the gas valve will close and the ignition cycle
will be repeated for a total of three attempts. If, after
the third attempt, the presence of flame is not detected,
the furnace will go into a lockout condition for one (1)
hour. It will then repeat the ignition cycle. This one (1)
hour lockout and retry will occur indefinitely.
· Thirty (30) seconds after the main valve is energized
the circulating air blower will be activated.
· The furnace will remain in operation until the demand
for heat is satisfied.
· Once the demand is satisfied the venter will shut off,
and the circulating air blower will shut off after the field
selectable time off is attained.
· The furnace will remain dormant until the next demand
for heat.
Dec 03, 2010 | Goodman GMS80903BNA Heater
Inductor blower comes on and runs then the ignitor glows flame comes up and burns for approx. 10-15 sec then goes out then fan comes on. Model number is PBKMLB12N0B0F I believe this is a goodman furnace.
I cleaned the sensor that was at the the right further most burner on my Goodman and it worked. got the answer to my problem here at fixya. My burner flame only lasted 5 secs before it shut off. Thanks to all who took the time to send me a response.
Nov 13, 2010 | Goodman Heating & Cooling
I have a goodman furnace model#GMT045-3A. when I turn it on the electronic pilot works fine and the furnace will start and run about 30-45seconds then shut off. I followed the insructions for restart but...
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Jan 26, 2010 | Goodman Heating & Cooling
My 8 yr old Goodman heater will ignite for 10-20 seconds then cut off, and then attempt over and over. Leaving our 2 bdrm condo cold. It did this last year, and all we had to do was change the filter. I...
Sounds like a flame sensor issue. It may just need to be cleaned. It is located either far right or far left in the burner box and has only one wire going to it. It will be in the flame of the last burner. If the flame can't get to it in a very short time the computer shuts the burner down. Make sure all burners are clean. You can use a can of air if you are careful near the igniter, it is very delicate. Here are some other ideas.
Dec 29, 2009 | Goodman Heating & Cooling
Have a Goodman GMT070-3B which the vent motor seems to be sticking. I took apart and cleaned the brushes and reassembled. The furnace will come on only after what seems like the vent motor comes up to...
The whole assembly must be replaced.
The sequence of operation is -
Combustion fan purges the heat exchanger. A pressure switch verifies combustion air fan is running. Usually a 30-45 second purge before the hot surface ignitor glows, or the spark ignition starts.
Gas valve opens after 10-15 seconds and main burners light. Control board monitors for flame and shuts gas valve after 2-3 seconds if main burner does not light.
If burner does not light, some boards repeat this for 3 tries, then locks out and is reset by cycling power.
Air blower comes on after another 30-45 seconds after main burner ignition.
Times may vary based on the specific controller board. A flow chart and timing sequence should be located somewhere on the unit, usually in the fan compartment.
Dec 16, 2009 | Goodman GMS90703BXA Heater
Furnace shut off after 3 time flame from pilot
Sounds like you may have a weak or bad flame sensor. If the circuit board does not sense a good flame it will not light the burners. Also if your furnace is 5 yrs or newer it should give you a fault on circuit board in the form of a blinking or a code itself.
Feb 15, 2009 | Goodman GMS90703BXA Heater
Goodman gmp125-5 burners ignite, then shut off after about 5 sec
One of two problems are happening here, your flame sensor is bad, your thermo pile or thermo couple is bad, or last is that the cap on the flue is blocking the exhaust from escaping
Feb 08, 2009 | Goodman GDS80904BNA Open Flame Heater
Blower works but no heat
If in fact you have the above listed furnace, you do not have a pilot but electronic ignition. You will need to remove the front cover on the furnace, tape down the door safety switch and then have someone help you by turning up your thermostat to a very high setting. Watch and listen inside the furnace. There should be some blinking going on at the control board followed by a small blower fan starting up. Then after 10-15 seconds there should be a click followed by an orange glow viewed thru the viewing window to the burner section. In a few seconds the gas valve should click and the burners will ignite. There is a safety switch that will sense flame and then keep the gas going to the burners. If it does not sense it, it will shut it off within 10 seconds. If all is well so far, your blower will turn on in about 90 seconds after flame. There is a diagnostic code chart on the back side of the access door if you get an error code (blinking) on the control board.
Always check little things like air filter, condensate drain and broken or loose wires.
Nov 05, 2008 | Goodman GMS90703BXA Heater
Goodman GMS90703BXA Heater Logo
825 people viewed this question
Top Goodman Heating & Cooling Experts
Dan Webster
Dan Webster
Paul Carew
Tim Whalen
Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others