Question about Zenith ZTG Nema-3R, 400 Amps Three Phase, Automatic Transfer Switch (ZN3NEMA3R400) UPS System
Zenith ZTX transfer switch, three phase 150 amp
Switch will not tranfer automatically. Generator indicator L E D's on panel are flashing red. Is the switch telling me something with the L E D s flashing?
Thanks
Bert
  • Jerupaja Apr 13, 2009
    unit in auto,didn't start during power outage
    Problem Solver:
  • 16 Answers
I suggest to call GE's 24x7 tech support team @ 1-800-637-1738, option # 3
www.gedigitalenergy.com/pq
Posted on Nov 08, 2009
If the s2 and load are flashing every couple of seconds that means your exerciser is set.
Posted on Jan 22, 2009
Automatic transfer switch not transfering power to home
YOU MAY WANT TO CHECK THE RELAYS THAT ARE IN THE TRANSFER BOX
Dec 15, 2013 | Generac Guardian 200-Amp Automatic...
I have a Taylor Perkins 150 KW generator on chicken houses. It will start on manual but not on automatic. Once started manually it won't transfer thru transfer switch.
Go the transfer switch and locate the 2 DC control wires that go to your generator for remote start.(On the remote start terminals) If you jumper these wires in the transfer switch and it starts, then the problem is with the transfer switch. If it still won't start check the wiring from the switch back to the generator, if all ok then suspect the generator control board. I would recommend you have an electrician do this, as there is line utility power in the switch and is dangerous !
Sep 21, 2013 | Taylor Cutler Hammer 3-Phase,...
The green lights that normally shows utility power available are not lit despite having 240v all the way through to the house. I had to manually swich it off. Control panel???
Hi Scott,
If this is a newly installed Automatic Transfer Switch (or "ATS"), stop. Call the installer and have them get it working properly. You do not want to start poking around and potentially void the warranty.
If this ATS has been installed earlier and has worked as expected before, and this is the first failure, then we can rule out an improperly connected ATS. I have looked at the manual and see table 9 on page 15 shows a troubleshooting guide. The second condition speaks to the failure to return to utility power due to "T" timer, auto exerciser, or S1 (left-most green LED) power quality / presence issue. It is this last S1 indicator that seems to be the issue. If it is not working, the other green LED (S2) will not light as the ATS will not close the contacts between the Utility and Load. This tends to make me believe the problem lies within the control panel as it is responsible for sensing not only utility power, but performs the synchronization or timing of the transfer of the load from one system or the other. This is needed as generator power is unstable until the generator speed has come up to speed and remains constant. Likewise, the utility sees a huge load when they restore lost power and this can cause some odd waveforms - those that most electronics do not like. Either way, they are power quality issues. Since they are two different systems, it is highly unlikely that they are synchronized. The controller helps to minimize the mismatched waveforms for a smooth transition.
This is a job for qualified personnel. You need to be careful as this system when shut down, might automatically start the generator. If you can't hear it - the potential for shock, burns or even death is present. Be careful - or better yet, call an electrician or the company that performed the installation.
Aug 30, 2011 | Zenith GE ZTX Series 200A Automatic...
Just finished installing a 20 KW Generac generator (fueled with natural gas). The included transfer switch will not automatically transfer to the generator, but transfers back to the utility without...
Check the connections on the tranfer relay and two coils. The two coils have blue wires. I have seen them come off from assembly or shipping its common. Each coil has two blue wires #8 and E1 with crimp steak ons and limit switches make sure there all pushed on all the way. Hope this helps
Mar 09, 2011 | Generac Guardian RTSE200A3 200 Amp...
How do you calculate low phase voltage of a three phase four wire system without useing voltmeter?
u can take three incadescent bulbs of same rating, connect them in 3 phase star connection, means 3 phase 4 wire connection..connect it across supply..the bulb connected across low voltage phase will glow dimmer than other two
Jun 19, 2010 | Zenith ZTG Nema-3R, 400 Amps Three Phase,...
What are some the problem if transfer switch dose not transfer when genarator cut in?
If the transfer switch is wired correctly, but for some reason it fails to switch over, even though the generator starts, this will not cause a problem or a safety issue. It will simply mean that no power from the generator goes to the house, and your house will still be connected to the utility company line. The generator will continue to run, but only with enough power to keep itself running at the proper speed. It will have no load on it, which is the same thing that would happen if everything in your house was turned off.
May 20, 2010 | Zenith GE ZTX Series 200A Automatic...
Generator available light rapid flashing
press the reset key(button) on the controller (asumming you have a R-M4 controller.) The R-M3 controller should have a reset button too.
Jan 17, 2009 | Zenith GE ZTX Series 100A Automatic...