The led indicator blinks 3 times on an Amana 90 furnace. What does this mean? The furnace won't fire.
Pressure switch open. Remove the small hose at the blower assy and gently **** on it. You should hear the switch on the other end of that hose change states. If not then it's the hose (cheap) or the switch (100 bucks but tough to find 2 years ago) or the wiring to/from or the control module. If it does do you have a bunch of white **** (the gasket) coming out of the black blower mount? I had to remove broken gasket and Permatex the seal to create the proper pressure; that's probably your problem as well.
Posted on Oct 03, 2008
Rheem Classic 90 FURNACE. Blower motor constantly running, even if t-stat is removed. Led blinks four times. PS closed, is the code. Not a psycho problem, I think it is the voltage transformer.
An LED that blinks four times followed by a two-second pause is signaling the pressure switch is closed when it should be open. The switch itself might be stuck, or the tubing that attaches the switch to the furnace's draft inducer might be blocked
Jul 13, 2016 | Heating & Cooling
My Xenon high efficiency furnace has a red blinking led light that blinks 4 times and my furnace will not light. What could be the problem?
Gas furnace fault or error codes for common furnaces - Gray ...
www.grayfurnaceman.com/-ifc-failure-codes.html
Each color will also flash a specific number of times to signify a specific error. ... 4 redcolored flashes may be signaling that the "high-limit" switch might be open. ... 3 green colored flashes on your furnace has the same meaning as 2 green colored flashes. ....If a system problem occurs, a blinking LED shows a fault code.Missing: xenon
7 Tips and Tricks to repair your Furnace DIY - YouTube
? 13:25
https://www.youtube.com/watch?v=rAtcvPqUsBA
Dec 18, 2012 - Uploaded by JRESHOW .
Flash sequence codes 1 through 11 are as follows: LED will turn "on" ... 4 RED FLASHES: This indicates that the main limit switchhas opened ... This no-light condition occurred 3 times (2 retries) during .... My furnace trane xe80 is only flashing once my manual says something about flame being locked out ...Missing: xenon ‎efficiency
Nov 21, 2015 | Heating & Cooling
Amana Air Command 90 furnace LED light blinks 3 times pause 3 times
TRI-COLOR (DSI LED) DIAGNOSTIC TABLE
No. of Red BLINKS
1 Flame sensed when no flame should be present
Verify the gas valve is operating and shutting down properly. Flame in burner assemble should extinguish promptly at the end of the cycle. Check orifices and gas pressure.
2 BLINKS Pressure switch stuck closed/ inducer error
Pressure switch stuck closed. Check switch function, verify inducer is turning off.
3 BLINKS 1st-stage pressure switch stuck open/inducer error
Check pressure switch function and tubing. Verify inducer is turning on the pulling sufficient vacuum to engage switch.
4 BLINKS Open limit switch Verify continuity through rollout switch circuit.
5 BLINKS Open rollout/open fuse detect Verify continuity through rollout switch circuit, check fuse.
6 BLINKS 1st-stage pressure switch cycle lockout If the first stage pressure switch cycles 5 times (open, closed) during one call for heat from the thermostat the control will lockout.Check pressure switch for fluttering, inconsistent closure or poor vacuum pressure.
7 BLINKS External lockout (retries exceeded) Failure to sense flame is often caused by carbon deposits on the
flame sensor, a disconnected or shorted flame sensor lead or a
poorly grounded furnace. Carbon deposits can be cleaned with
emery cloth. Verify sensor is not contacting the burner and is locatedin a good position to sense flame. Check sensor lead for shortingand verify furnace is grounded properly.
8 BLINKS External lockout (ignition recycles
exceeded where flame is established and then lost)Check items for exceeded retries listed above and verify valve is not dropping out allowing flame to be established and then lost.
9 BLINKS Grounding or Reversed polarity Verify the control and furnace are properly grounded. Check and reverse polarity (primary) if incorrect.
10 BLINKS Module gas valve contacts energized
with no call for heat Verify valve is not receiving voltage from a short. If a valve wiring is correct and condition persists, replace module.
11 BLINKS Limit switch open - possible blower
failure overheating limit Possible blower failure, restricted air flow through appliance or duct work. Verify continuity through limit switch circuit and correct overheating cause.
12 BLINKS Module Ignitor contact failure Fault code indicates the module ignitor contacts are not functioning
properly. Replace module.Solid Module - internal fault condition Module contacts for gas valve not operating or processor fault.
Reset control. if condition persists replace module.
3 double 2nd-stage Pressure Switch Stuck Open/Inducer Error
Check pressure switch function and tubing. Verify inducer.
Nov 11, 2013 | Patton Electric Patton PUH680-U Electric...
Bryant furnace plus 90 led code is blinking once then 3 times fast. What does it mean?
these codes are on the inside panel of the front cover of the furnace. lift off and look inside.there should be a code explain chart on the panel by the light. this panel will need to be replace correctly for the furnace to work as there is a door switch.
Jan 31, 2011 | Heating & Cooling
I have an amana dms 90904cms furnace ..the fan runs but no heat. I opened cover and saw the red led blinking 3 times code says open pressure switch. what does that mean?
Open pressure switch is when your vent motor comes on it has to get a certain vacuum pressure or it won't ignite furnace. There should be some little black hoses connected to vent motor and maybe into heat exchanger, running to these pressure switches. Pull hose off one end and make sure hoses are not kinked or some times if hoses have sag in them they can fill with water. Other causes are if venting is obstructed or pressure switch is defective, especially if it got moisture in it.
Jan 26, 2011 | Heating & Cooling
On a 80% Rheem upflow furnace... The AC works fine but when switched to heat nothing happens. "OK" LED is on solid, second LED is blinking 3 times, "FLAME" LED is not on at all. What can be the problem?
Hello ANGUS,I think 3 blinks is open pressure switch,try taking the door off the furnace.The upper left hand side is a round black box with a hose attached to it .Gently tap the switch(box) and turn off power for 2 seconds andback on,then call for heat.the blower door has a sticker inside that tells you just what the blinks mean.
Aug 10, 2010 | Heating & Cooling
I have an Amana Air Comand Gas furnace/AC, it's 4
Hi, If you are talking about an led light at the furnace, and it is blank, it should have a 3 to 5 amp fuse that plugs into the board. Pull it and check to see if the metal element is blown or burnt. If so, replace it. If you are talking about some other red light, please let me know. It sounds as though you have lost the 24 volt control voltage, so see if it has a fuse on the board. Keep me posted.
Shastalaker7
Dec 31, 2009 | Heating & Cooling
Induced Draft Blower Not Blowing- 3 Blinks on LED
Your doing well just right. When the call for heat is on the draft motor gets a call from the board to come on. When this happens if no voltage is present at the motor then you ahve abad baord. Replace it.
Nov 28, 2009 | Heating & Cooling
Ruud achiever 90 plus won`t start
Check the data information on the unit there should be a troubleshooting guide that tells you what the two lights blinking once means. hope this helps.good luck. normally found with schematic
Feb 05, 2009 | Ruud UBHC Air Conditioner
My Amana Gas Fired Air Furnace (80) failed to come on with warm air. Blower works but cold air only? Is there an obvious problem here?
first, clean the flame sensor, does the draft motor come on?  could be ignition control board failure
Nov 15, 2008 | Amana Heating & Cooling
Heating & Cooling Logo
581 people viewed this question
Top Amana Heating & Cooling Experts
Dan Webster
Dan Webster
Bill Long
Are you an Amana Heating and Cooling Expert? Answer questions, earn points and help others