GOODMAN CMA80905CXBA FURNACE. INDUCTION BLOWER NOT ENERGIZING. GETTING 3 "BLINKS" FROM DIAGNOSTIC LIGHT (LOW PRESSURE SWITCH OPEN). THE A/C WORKS & THE BLOWER FAN COMES ON WHEN THE STAT IS IN THE HEAT MODE WITH THE FAN SWITCH ON. WHILE THE FAN IS ON , THE DIAGNOSTIC LED STILL BLINKS A CODE OF 3. THIS IS NOT A CONDENSING FURNACE. I BYPASSED THE STAT (W & R)TWISTED TOGETHER---SAME RESULT---DIAG LED COMES ON STEADY, THEN FOUR CLICKS, AND BACK TO THE CODE OF 3 BLINKS. CIRCUIT BOARD???? OR 120VAC NOT REACHING THE INDUCTOR FAN?? BATTERIES FRESH IN STAT. HEAT WAS FINE LAST WINTER---INSTALLED A/C MAY 08. THAT WORKED FINE. NOW NEED HEAT AND THIS HAPPENS. HIGHLY APPRECIATE ANY HELP. FYI...THE A/C IS GOODMAN ALSO. ALL PURCHASED AT THE SAME TIME, LATE SEP 07. DIDNT INSTALL A/C THEN BECAUSE WEATHER WAS SOON TO CHANGE.
  • FALCONHAWKER Oct 02, 2008
    gonna try RIGHT NOW! Thanx for your thoughtful response.
    Tried it. Nothing. I thought the darft motor has to come on first to close the switch. The draft motor isn't coming on.
  • 182 Answers
The pressure switch is closed before the draft motor closes it.the board is telling you that this is not right.pull the wire(either) off of the pressure switch to see if furnace tries to light.if it does,you should replace the pressure switch.
Posted on Oct 02, 2008
Furnace will not ignite.
I think you are talking about draft induction pressure switch operation. Make sure the metal orifice located on the draft induction blower is clear. To check, remove the rubber tubing end at the pressure switch and blow into the tubing. It should be easy to blow through it. If it is plugged, remove the tubing from the blower orfice and use a paperclip, inserting it into the orfice to clear the opening. After repairing, and all is hooked up, retry the furnace start up procedure. If the code comes up again, replace the pressure switch.
Dec 17, 2014 | Goodman Manufacturing...
Furnace problems
On - OK
1 Blink - Ignition failure. Check Gas flow, gas pressure, gas valve, flame sensor.
2 Blinks - Closed pressure switch. Check pressure switch (stuck in closed position).
3 Blinks - Pressure switch - failre to close. Check venter, pressure switch, vent blockage.
4 Blinks - Open limit switch. Main limit or aux limit are open. (My comment - Means overheating in chamber. Often result of blocked intake air. Bad filter. In my case, plastic wrap had been sucked into the intake. )
6 Blinks - False flame sensed. Check sticking gas valve.
Rapid continuous blinking - Incorrect twinning, incorrect primary polarity. Reverse transformer secondary leads, reverse primary wires.
Closed pressure switch can be from dirty combustion vents, bad chamber pressure - like missing screws, maladjusted gas pressure, failing pressure switch, loose hoses, moisture in the hoses or fan blades The switch need to be closed to ge the unit to work
Jan 23, 2008 | Goodman GMS90703BXA Heater
Protech 62-24084-02 troubleshooting
62-24084-02 LED CODES
POWER LED - GREEN
ON - Normal
OFF - No power to board
OK LED - GREEN
One Blink - One hour retry delay
Two Blinks - Pressure switch failure (remains open)
Three Blinks - Limit switch fault
Four Blinks - Pressure switch failure (remains closed)
Five Blinks - Twinning fault
FLAME LED - YELLOW
ON - Good flame
Rapid Blink - Flame present with gas valve de-energizing
Slow Blink - Marginal flame
Jan 01, 2014 | Protech Rheem/62-24084-82-1PK - Integrated...
Goodman dependable 92,7years old. Furnace works sometimes. Checked out by qualified technican. no problem found. Constant checks shows troubleshooting light blinks three (3) times. Help please. 3...
This indicates a open limit switch on the furnace, the heat exchanger is getting to hot therefore the limit switch is opening and not allowing the furnace to work properly. Did the techinician check the limit switch on the unit?
Dec 30, 2010 | Goodman GMS90703BXA Heater
When i start furnace fan starts comlete purging cycle but not igniting indicator light blinks rapidly
though your draft induced blower goes through its cycle, your pressure switch may not be proofing to open the main gas valve.
Nov 28, 2010 | Goodman GMS80453ANA Open Flame Mid-Size...
Goodman furnace model#GCH90904CXAB the red light
This model is equiped with a diagnostic error control. Take off the front panels and look for a wiring diagram pasted on the reverse side of the panels. On this diagram there will be a chart telling you what 4 blinks represent and where to start looking for the issue. I suspect the air filter may be dirty or the pressure switch may be bad, however make sure the condensate hoses are free of any debris. Good luck to you!
Apr 25, 2010 | Goodman Heating & Cooling
Heater exhaust blower comes on ignitor lights but it doesn't seem to get gas everything works but no flame and blower won't kick on the unit is brand new and was working this morning then stopped
This furnace should have a trobleshooting diagnostic led flashing light. Each blink (for example 3 blinks means open limit switch) has a particlur meaning. On the bottom panel has an explaination on what the blinks mean. But in the meantime check 24v at the gas right as the ignitors light. If you have 24v and the gas valve doesnt let the gas thru then the gas valve might be defective. I usually put 24v dircetly to the gas valve for 2-3 seconds to see if gas will come out. It is loud enogh to hear as well as smell. If you dont have 24v as the ignitor tries to light then check the air pressure switch. Also follow the wire off the gas valve. One is to ground. Make sure the gas valve is grounded. Follow not the grounded wire but the other one. Find out where the 24v power stops.
Mar 24, 2010 | Goodman GDS80703ANA Open Flame Mid-Size...
I have a Goodman GMPN080-4 furnace. The light on the board blinks 3 times. The furnace won't light at all. What could be the problem?
Hi 3 blinks should mean it is the pressure switch there should be a code in the manual or inside of the door
Jan 30, 2010 | Goodman Heating & Cooling
Need to find the pressure switch on my goodman furnace
It's mounted onto the gas valve. It will be a button or lever that you have to push in or down, depending on the style.
Nov 20, 2009 | Goodman GDS80904BNA Open Flame Heater
No heat!, light blinks 3 times
Make sure the inducer motor is free of condensation and that all water is able to drain out. Unfortunately your furnace is a lower-grade “builders” model and does not have the same quality of components and workmanship as a Carrier or American Standard furnace. Prior to these failures, It was about 1/2 the price of the units mentioned. And the warranty drops off quickly. You get what you pay for.
Contact Goodman to see if they will cover the cost of your parts at 1-877-254-4729 US only. Their own motto is “Quality Makes the Difference”. It sure does.