A carrier furnace
I am working on a carrier furnace a when a call for heat the inducer motor do not come on. I replace the control board for the inducer motor and check the volts to the control board and it show 26 volts and the relay don't allow the 120 volts for the inducert motor to run. what can be the problem?
  • 550 Answers
Check the relay
the primary should have a low resistance
there should be a distinct click when 24 volts is applied to the primary
the secondary should be conductive when the primary is energized (contactors can corrode)
not a solution something to check
Posted on Oct 02, 2008
I am working on a m/n 58SS080-bc carrier the .When a call for heat the inducer motor didn't come on replace the control board for the inducer motor and it still didn't come on .Icheck for the low voltage...
hi there,
is there an inverter board or a thermocouple in this unit? sounds like you have too much voltage coming to the board. can you measure the voltage to the motor?
Oct 02, 2008 | Carrier Heating & Cooling
Need to find a replacement part
Here you go Angela
1149097 Draft Inducer Assembly - AllParts Heating
  1. Cached
  2. Similar
Draft Inducer. 1149097 draft inducer for Heil, Tempstar, Arcoaire, Whirlpool & Comfortmaker brand model furnaces. This part replaces old part number 1008416.
Arcoaire Furnace Motor Parts: Fast Shipping
  1. Cached
  2. Similar
Furnace draft inducer assembly. The draft inducer motor draws air into the burner and exhausts it out the flue. If the draft inducer motor is defective, the furnace ...
Arcoaire Furnace Parts: Fast Shipping
  1. Cached
Direct Factory Replacement Inducer Blower Motor Used in 90 ... > ... > Oem Direct Replacement Models > Arco Aire
  1. Cached
  2. Similar
Direct Factory Replacement Inducer Blower Motor Used in 90% Furnaces. ... Comfortmaker, Intercity Products Snyder-General, Heil, Tempstar, Arcoaire Draft Inducer Blower Motor. ... Used in ICP Equipment Models: ... GUH125A016CIN
1149097 - Arcoaire Furnace Draft Inducer / Exhaust Vent Venter Motor ...
  1. Cached
1149097 - Arcoaire Furnace Draft Inducer / Exhaust Vent Venter Motor - Fasco Replacement: Replacement Household Furnace Motors: Industrial ... Draft inducer motor for arcoaire model guh125a016cin Google Search
Nov 27, 2016 | Heating & Cooling
Have an older Coleman mobile home furnace (Mdl 8665D766). Both blower fan and booster motor work fine; however, during heating, booster motor will keep constantly running after system cycles through
The booster motor? Do you mean the inducer motor that helps push the exhaust? If the inducer motor won't shut off when the thermostat is satisfied and everything else does shut off, it sounds like the contacts on the relay that powers the inducer are at fault
Feb 03, 2018 | Coleman Heating & Cooling
Changed inducer motor, now furnace will not ignite and gives code 31
since there is no model number to go by, let's go generic. Most inducer motors have some way of "proving" it is running to the control board. It may have a centrifugal switch in it or it may have use some type of air pressure switch. The centrifugal switch will usually have 2 wires other than the power wires and most of the time, go to the rear of the motor. The air switch usually has a small rubber hose that pushes onto it and is connected to the fan housing.
Aug 06, 2017 | Carrier Heating & Cooling
I have a carrier furnace the control board keeps coming up with differ t led coxes ifiI reset it it works a couple times then flashes a new code had four different codes come up so far 21 22 31 34
Have to know the model and serial of the furnace.
locate code list usually inside or on the back of a door.
Operation sequence= call for heat--inducer blower motor--makes pressure switch--signals board to bring on hsi--after a set time gas valve opens and you have ignition--main blower motor comes on after a set time
Feb 05, 2014 | Heating & Cooling
Carrier Furnace won't start up
Sequence of events: call for heat at T-stat, inducer motor turns on, negative pressure created in heat exchanger closes pressure switch, pressure switch control wire runs through all safety's (these must all be in closed/safe position) if ok then glow plug lights. Time delay then gas valve opens, flame verified by "flame rod" t-stat = :)
Apr 22, 2013 | Heating & Cooling
Problem: Your furnace will not ignite the gas to produce heat for your home. When a furnace has a bad ignitor what I see most of the time is the following sequence of operation:
1. Thermostat calls for heat.
2. Draft inducer motor starts.
3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes.
4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution: You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. Please see "limits, rollout switches & furnace control boards" further down on this page. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Nov 25, 2010 | Heating & Cooling
Lennox pulse 21 furnace - nothing runs on but control board tries
you will need to verify voltage from the board to the inducer. If you have the installtion manual there is a flow chart for the sequence of operation of the furnace.
The basic sequence is:
1. thermostat calls for heat
2. inducer motor starts and runs for a pre-set amount of time
3. the pressure switch closes and allows for ignition trial
4. ignition is proved back to the board allowing the system to operate.
Verify 120VAC to the inducer motor upon call for heat from stat, if you have 120 at the leads that connect to the inducer and it does not start , the motor is faulty. If the inducer starts use a voltmeter across the pressure switch terminals, a voltage reading of 0 VAC will verify contact closure and ignition should occur.
The pulse furnace was under a factory recall due to breaches in the heat exchanger, unfortunately for you, the Lennox Corp. has ended the program that allowed for an allowance / furnace for replacement. To test the heat exchanger a special kit is required from lennox that will verify integrity of the heat exchanger. (If the heat exchanger seal has been comrimised the pressure switch will not prove and the igniton sequence will be interupted and cause the system to go into "lock-out" mode).I know this is probably not what you wanted to hear. Hope this helps, please list as "very helpful" if it did
May 08, 2010 | Heating & Cooling
Heat not coming on carrier gas pack code 31
code 31 indicates pressure switch did not close or reopened during the heat cycle....1st thing to check is the inducer motor,,this is a small motor that turns a small blower wheel that draws the exhaust gases through the furnace and blows them into the vent pipe....1st locate the inducer assembly,,most easily identified by the small plastic fan blade that cools the inducer motor as it runs..1st turn off tstat and turn off furnace power switch..then turn on furnace switch,then set tstat to heat,set the temp above room temp by 5 degrees...remove the furnace front cover,locate the inducer motor,,if it isnt turning,but is warm or hot after a minute or so,likely the inducer motor is bad..if it isnt turning and isnt warm after 1 minute,then likely the main control board is bad,,not turning the inducer motor when it should,,,,,if the inducer motor is running,,then the pressure switch isnt closing,, could be a bad pressure switch but more likely there is a problem with the venting...some possible problems that would cause the pressure switch not to close in an 80% eff furnace [metal vent pipe] are: [1] a blockage in the vent pipe,base of chimney,dead bird at the furnace where vent connects to furnace or down inside the inducer assy,accessed by removing vent pipe from furnace....if all clear the chimney could be blocked up inside,,is the draft good when vent is removed from base of chimney?..if furnace is a 90%+ type [pvc plastic vent pipe],,then check the intake pipe at the furnace by removing it where it attaches to top of the intake clogged with anything?..then check the intake and exhaust pipes outside for blockages,,including ice/frost/snow at the exhaust pipe outlet..
Jan 26, 2009 | Goodman GMS90703BXA Heater
Heating & Cooling Logo
154 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Tim Whalen