Question about Carrier Heating & Cooling
I am working on a m/n 58SS080-bc carrier the .When a call for heat the inducer motor didn't come on replace the control board for the inducer motor and it still didn't come on .Icheck for the low voltage to the inducer control board and it did have 26 volts to the board . what could be the problem?
    Sergeant:
    Champion:
  • 435 Answers
Are you sure if the  inducer motor is working?
How did you test it? I believe the problem is with the inducer motor since it didnt turn on even after fixing the control board and also the voltage is fine.
Posted on Oct 02, 2008
    Sergeant:
  • 409 Answers
is there an inverter board or a thermocouple in this unit? sounds like you have too much voltage coming to the board. can you measure the voltage to the motor?
My carrier model # 48ss-036100331 induced-draft motor will not start
On some of those inducer motors there is also a capacitor in the blower compartment on the left side of the burner section. It is possible that if you have 230v coming from the board CM terminals and if the motor is new maybe you have a bad capacitor in the blower section. Follow the wires to the capacitor and check microfarad reading to that capacitor. Caution there maybe 2 in this area but one is for the indoor blower motor and the other will be for the draft motor. The blower capacitor may be somewhere between 10 or 15 mfd but the draft inducer capacitor will be around 3 mfd. hope this helps
Feb 19, 2016 | Carrier Heating & Cooling
Changed inducer motor, now furnace will not ignite and gives code 31
since there is no model number to go by, let's go generic. Most inducer motors have some way of "proving" it is running to the control board. It may have a centrifugal switch in it or it may have use some type of air pressure switch. The centrifugal switch will usually have 2 wires other than the power wires and most of the time, go to the rear of the motor. The air switch usually has a small rubber hose that pushes onto it and is connected to the fan housing.
Aug 06, 2017 | Carrier Heating & Cooling
Carrier error 42 on model 58MVP080.... is it the inducer motor or control board?
Low pressure sensor fault. Check dc voltage between white and black cable on plug. Multi V: 1 Vdc = 4 bar up to 5 Vdc = 32 bar
Oct 19, 2011 | Carrier XHB123D X/Y Series Heat/Cool Air...
I have a 15 ton carrier gas pack at work with inducer motor and spark igniter with hall senser ..showed error 6 flashes on igc board which the drawing said was inducer motor or hall senser...
The error code is always right. Sometimes misleading, but in 15+ yrs I've seen, always right. I'm not familiar with a Hall Sensor. If this is a remote sensor, as in a remote location that senses in the hall and not at the tstat then I know what you're calling a hall sensor. Make sure your IDM is working and closing the air proving switch. And that no other safeties are in that circuit. Check continuity to the remote sensor wiring and all connections? I've seen hot surface ignitors look fine and not work, but pulled a new off the truck and the new worked. All else fails, remote sensors are tough to get a good ohm value due to a temp difference affecting the ohms, replace it. I'm not sure why your "drawing" would relate the IDM to a remote sensor so I'd focus on the IDM and follow the voltage trail.
Apr 03, 2017 | Carrier Heating & Cooling
Carrier 48sx gas pack. Won't turn on. No smell. No igniting sound. Blower fan works. How do I troubleshoot this?
Remove the panel from the heater section, you will need to watch what happends as there is a call for heat. There may be a light on the control board that lights up or blinks to indicate a call for heat. The inducer blower (exhaust blower) will start. INn a few seconds after the blower starts, the igniter will glow orange. After a few more seconds the gas valve should open and the burner will ignite. If the inducer does not run, you may have a bad motor or control board. If the igniter does not glow, you could have a bad pressure switch, bad pressure switch hose or a broken igniter. If the gas valve does not open, you may have a bad control board or bad gas valve. If you get no light on control board, bad fuse, bad thermostat or bad control board.
Jan 03, 2011 | Heating & Cooling
Where does the 3 prong inducer plug into? Carrier Weathermaker Model 58SXAO80-GG Serial 1490A02296
Hi, it would either plug into the circuit board/control board, or have a connector of the same, either male or female it would plug directly into. This is a 120 volt inducer motor. Look for the other end of the plastic plug.
Sincerely,
Shastalaker7
A/C, & Heating Contractor
Sep 29, 2010 | Heating & Cooling
Lennox pulse 21 furnace - nothing runs on but control board tries
you will need to verify voltage from the board to the inducer. If you have the installtion manual there is a flow chart for the sequence of operation of the furnace.
The basic sequence is:
1. thermostat calls for heat
2. inducer motor starts and runs for a pre-set amount of time
3. the pressure switch closes and allows for ignition trial
4. ignition is proved back to the board allowing the system to operate.
Verify 120VAC to the inducer motor upon call for heat from stat, if you have 120 at the leads that connect to the inducer and it does not start , the motor is faulty. If the inducer starts use a voltmeter across the pressure switch terminals, a voltage reading of 0 VAC will verify contact closure and ignition should occur.
The pulse furnace was under a factory recall due to breaches in the heat exchanger, unfortunately for you, the Lennox Corp. has ended the program that allowed for an allowance / furnace for replacement. To test the heat exchanger a special kit is required from lennox that will verify integrity of the heat exchanger. (If the heat exchanger seal has been comrimised the pressure switch will not prove and the igniton sequence will be interupted and cause the system to go into "lock-out" mode).I know this is probably not what you wanted to hear. Hope this helps, please list as "very helpful" if it did
May 08, 2010 | Heating & Cooling
Cycleing,
You are referring to the inducer motor that is kicking on and off. It is probably a limit switch that might be triggering it to go off and on over and over. It could possibly be the board but I highly doubt it since the ac works just fine. It can also be a short in the wiring going to the inducer motor as well or the inducer motor is going bad. Without checking it out myself with a voltage meter, it's hard to pinpoint exactly what is causing the issue but I highly doubt it is the main board. Get a second opinion.
Mar 19, 2009 | Carrier Heating & Cooling
Induced draft motor
The inducer motor is what takes the cabonmonoxide out of the house from the unit and should not be bypassed
Mar 08, 2009 | Carrier Heating & Cooling
A carrier furnace
check the relay
the primary should have a low resistance
there should be a distinct click when 24 volts is applied to the primary
the secondary should be conductive when the primary is energized (contactors can corrode)
not a solution something to check