Question about Goodman GDS80904BNA Open Flame Heater
Ignition failure after three attempts then sits for an hour.
My Goodman furnace is less than 3 years old. Occasionally, not always, but now with increased frequency, My furnace will fail ignition and go into the one hour sit and reset mode. The exhaust fan comes on, ignition stick starts glowing, I here a click, then the glow stick goes out. The furnace will not fire. After three attempts, it goes into lockout state for one hour. There is no obstruction in the exhaust stack, and I have a 6" air inlet duct that stops 18" off the floor bringing in fresh air from the attic air space into the furnace room. The attic air is cool, and the inlet pipe is relatively near a gable vent to bring in outside combustible air. The inlet duct is approximately 30" from furnace. Any help will be greatly appreciated. Thanks
  • 1 more comment
  • TSOWP Nov 25, 2008
    Fan comes on, Ignition Glows but does not light the gas. GMP075-3
  • Anonymous Feb 14, 2009
    I have the same issue.  How much would a gas valve cost approximately. anyone know -  Angie
  • Melbe Mar 01, 2009
    problem turns out to be a bad connection on the main plug into the circuit control board. You need to alleviate stress off the plug by the weight of the wires, in order for everything to fire good.
Try cleaning the burners and or adjust the distance the igniter is from the actual burner .
Posted on Nov 14, 2011
  • greg V. Nov 14, 2011
    Do you have good gas pressure up to, or any pressure to the inlet side of your gas valve?
    Problem Solver:
  • 15 Answers
If your igniter comes on but no ignition, that eliminates the possibility of a bad or clogged pressure switch, high limit or flame rollout switch. Sounds to me like you have a control board, or a gas valve going bad. Could even be some loose, corroded, or faulty wiring. Before the igniter comes on the furnace does a self diagnostics to ensure everything is working, or the furnace will not make it to the igniter sequence. Inducer motor, pressure switch/s, limit controls are closed…then comes on the ignitier, gas valve opens, pilot runners and burners ignite, flame sensor detects the flame, blower comes on and all operations are working.
Hope this helps
Posted on Dec 02, 2008
Furnace will not ignite.
I think you are talking about draft induction pressure switch operation. Make sure the metal orifice located on the draft induction blower is clear. To check, remove the rubber tubing end at the pressure switch and blow into the tubing. It should be easy to blow through it. If it is plugged, remove the tubing from the blower orfice and use a paperclip, inserting it into the orfice to clear the opening. After repairing, and all is hooked up, retry the furnace start up procedure. If the code comes up again, replace the pressure switch.
Dec 17, 2014 | Goodman Manufacturing...
Ignition failure.
if furnace fires up then immediatly shuts off check the flame sensor. make sure it is sitting far enough inside the burner box and has proper continuity. if ur getting ignition failure without having furnace fire up, check proper voltage to hot surface igniter, continuity within igniter
Dec 05, 2013 | Heating & Cooling
Problem with Goodman furnace electric ignition
Power is there, or no lights would blink. Steady blinking or flashing three times, stop, three times Etc
Nov 23, 2011 | Goodman Heating & Cooling
Furnace GMS9/GCS9 Cycles twice and then fires up most of the time and then it won't fire and shuts down. To restart it We have to shut the 110/115 power off for a few seconds and turn it back on and it...
Furnace ignition controls will attempt to light the furnace 3 times with several minutes delay between each attempt. If it fails to light or the ignition module fails to detect it lit after the 3 tries, the module will lock out and require a "Hard Reset" to try again. It is a common feature in nearly all newer furnaces intended to let you know you have a serious problem. You should call a service technician for this because there are a number of things that may be causing this flame failure. Please grade my answer on how much I have helped you. Thank you for the opportunity. Roger
Apr 04, 2011 | Goodman Heating & Cooling
My inducer motor failed. What are 2 or 3 primary causes of failure in a 6 year old furnace?
The problem is called planned failure...it seems that most of the inducers will fail in that 6 year period no matter what you do... you can attempt to lubricate the bearings but it is very difficult and the heat from the usage gets to them....
Actually I have seen many fail in less time...most do not go that long... sad...
heatman101
Feb 23, 2011 | Heating & Cooling
Goodman dependable 92,7years old. Furnace works sometimes. Checked out by qualified technican. no problem found. Constant checks shows troubleshooting light blinks three (3) times. Help please. 3...
This indicates a open limit switch on the furnace, the heat exchanger is getting to hot therefore the limit switch is opening and not allowing the furnace to work properly. Did the techinician check the limit switch on the unit?
Dec 30, 2010 | Goodman GMS90703BXA Heater
I installed a new goodman unit this past spring. It seems to work ok to good in the day time but the tempature is warmer so we do not need as much heat. At night I know the thermostat is coming on. I...
Heating Mode (Goodman Service Manual)
· The furnace control checks for an open main limit (this
limit is normally closed). If the limit is open, the furnace
will remain inoperable until the limit is closed. During
an open limit the circulating air blower will be
energized. The status light will blink four (4) times.
· The room thermostat reacts to a demand for heat.
· The control will then check to insure that the vent
pressure switch is open. If, at this point, the vent
pressure switch is closed the control will blink two (2)
times and will remain inoperable until this situation is
corrected.
· The venter blower is energized.· The vent pressure switch will close when it detects a
pressure in excess of its setting. If the pressure switch
fails to close the status light will flash three (3) times.
The sequence cannot continue until the pressure switch
closes.
· After a pre-purge of about ten (10) seconds the electronic
ignition device will be energized.
· After a slight delay the gas valve will open.
· The burners will ignite and the flame sensor will detect
the presence of flame. The ignition device will
deenergize. If the sensor does not detect the burner
flame, the gas valve will close and the ignition cycle
will be repeated for a total of three attempts. If, after
the third attempt, the presence of flame is not detected,
the furnace will go into a lockout condition for one (1)
hour. It will then repeat the ignition cycle. This one (1)
hour lockout and retry will occur indefinitely.
· Thirty (30) seconds after the main valve is energized
the circulating air blower will be activated.
· The furnace will remain in operation until the demand
for heat is satisfied.
· Once the demand is satisfied the venter will shut off,
and the circulating air blower will shut off after the field
selectable time off is attained.
· The furnace will remain dormant until the next demand
for heat.
Dec 03, 2010 | Goodman GMS80903BNA Heater
Goodman furnace intermittently fails to ignite. Will flash code for ignition failure. Always relites when reset. Tends to happen much more often after hours on non use. During weekdays when the thermostat...
I do not have the figures with me at this time. If the ignitor is slightly out of proper resistance range, it may not be getting hot enough the first time it tries after being idle for a while. I would need my chart from work and the model of the unit, but have your last tech check that. They can call for the proper resistance to the Goodman tech line at 888-593-9988. And, the pressures should be 11-13" w.c. input and 10" out to the manifold when valve is open. If the input pressure is higher than 13, the valve diaphram could intermittently lock up.
Jan 03, 2010 | Goodman Furnace Draft Inducer Blower ...
Main Fan won't turn off even with thermostat removed. Burner not
There is a chart with the wiring diagram and othere charts that will tell you what the 6 blinks are for. That should tell you what is wrong and what part you need. Sounds to me like the board has an issue or the gas valve is locked out.
Jan 10, 2009 | Goodman GDS81155CNA Open Flame Mid-Size...
Goodman GMP075-3 ignition problem
Goodman gmp075-3 gas furnace and the flame cycles for 4 sec
Oct 01, 2008 | Goodman GDS80904BNA Open Flame Heater
Heating & Cooling Logo
786 people viewed this question
Top Goodman Heating & Cooling Experts
Dan Webster
Dan Webster
Paul Carew
Tim Whalen
Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others