Question about Goodman Heating & Cooling
Furnace completes cycle but the (24volts)wont keep the gas valve on.
    Scholar:
  • 121 Answers
Depending on which model you have there is a fan limit switch or a fan control or pc board that will bring the fan on once the furnace warms up some so that it doesn't blow cool air. This could be malfunctioning or the blower it;s self is malfunctioning which could be a fan relay, compasitor, or the blower motor it's self.
Posted on Sep 29, 2008
York Diamond 90 furnace blows cold air
There maybe a few issues. They have multiple safeties on furnaces. With this in mind this process to find the problem would take a Technician to check these safeties. It could be a flame sensor or thermocoupler each senses a flame or heat to keep the gas going. Also the damper for the flue must open for the gas to stay on. There may be more safeties on this and each safety sends a 24 volt current back to control module in order for the gas valve to stay open. If these aren't being met it will try around three times and go into a lock out mode which will keep gas shut off entirely.
Feb 21, 2012 | Heating & Cooling
20 year old gas furnace with hsi. I have replaced the draft inducer, control unit and the gas valve. The hsi is working but the gas valve does not open or opens only one in twenty tries. There is 26v...
Test for voltage and an amp draw on the gas valve while it should be energized, see if the power(24volts) is present and if so any amp draw, an amp deaw says its trying to work,
May 28, 2010 | Heating & Cooling
I HAVE A RUUD SILHOUETTE II GAS FURNACE. The glow rod glows bright, the fan whirrs for 30 seconds there is a click and nothing happens...the fan stops. No flame...nothing.??
this can be a few things. tonight, i fixed one with the same symptoms and it ended up being the gas valve was bad and the gas pressure on the outlet side was only 1 in water column on an LP furnace. That is one thing and would have to be checked with a manometer. The other is the board may not be sending 24volts to the gas valve telling it to open. hope this helps
Jan 05, 2010 | Ruud UBHC Air Conditioner
Yokr gas furnace will not start up
You could have the gas co to check to preassures at or before the unit. Too low or high a preassure and the gas valve cant regulate the proper flow>>Natural gas to the house needs at least 5"-wc psi ---to the gas valve needs 7.5"--wc and while its calling for heat the orrifice needs 3.5" -wc psi! Propane needs 11" wc psi to the valve on the unit and 11' -wc psi to the inside furnace.
Dec 21, 2009 | Heating & Cooling
My unit cycles on glow coil comes on and still no gas comes check to see if i had 24volts to gas valve when call for and it does but still wont open
Check to see if you have gas pressure coming to the gas valve. If you have that and the gas valve is getting 24V then it should work. If not then the gas valve needs to be replaced. This is not uncommon for them to fail.
Nov 12, 2009 | Goodman GMS90703BXA Heater
Won't light
If you can see the ignitor coming on and the furnace will not fire, if you have a elect. meter, see if you have 24volts at the terminals on the gas valve right after the pilot lights or glow plug whichever. you should hear the gas valve click when pilot is on and have 24volts at the valve at that time. If you do, then the valve is bad.If you don't have 24 volts, then check the stat for 24 volts. A safety may have tripped also. Try these things first and let me know. Good Luck, Shastalaker7
Nov 07, 2009 | Heating & Cooling
Draft inducer starts Hot surface ingination glows, gas does not come out of gas valve, repaeats 3 times furnace shuts off
The problem is you're Gas valve. If you have a volt meter, set it above 24 volts ac.When the Hot surface ignition glows, have you're meter on your gas valve terminals. Hold them there through the complete cycle, and you should have 24volts which you will, showing with power going to it, it will not open, the coil is burned out. Do not try and repair it! This has to be replaced.When the Gas valve is ready to open, you will hear a click.No gas, bad coil.This will solve you're problem, I have replaced so many of the MGV's. Good Luck, and please let me know, Thanks Shastalaker7
Nov 05, 2009 | Air Purifiers
Goodman ac/gas furnace unit mdl. # gmp075-4
i HAD THE SAME PROBLEM, TURNS OUT IT WAS THE FLAME SENSOR, CLEANED IT, AND ALL WAS GOOD
Nov 27, 2007 | Cozy (W352E) Heater
Heating & Cooling Logo
80 people viewed this question
Top Goodman Heating & Cooling Experts
Dan Webster
Dan Webster
paulcarew
Brandon Berry
Brandon Berry
Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others