Question about Coleman Heating & Cooling
Furnace come on then fan stops while burner still is on, then fan comes on for 1 min. and goes off over and over
    Scholar:
  • 121 Answers
This could be a couple of things, first is the fan limit switch. Make sure your fan limit is set at the correct settings, there is a fan on setting and a flame shut off setting located on the front of air handler inside the front cover. Usaully set at 140 fan on 200 gas shut off. You do not say what unit you have so this could be a pc board or module. Second this could be the blower it's self over heating and shutting down, feel if motor is gettig hot. This could be a run cap. or motor it's self. But it is more than likely the limit switch.
Posted on Sep 29, 2008
  • Edward Boukater Oct 01, 2008
    I don't understand how you can sy this is not appropriate I've been on the a/c heating business 30 yrs. Is there some other info. I'm missing.
Goodman furnace Model GDS80703AXBB -fan comes on then igniter light comes on, then burners turn on but shut off right away and wont stay lit. Now igniter light wont come on so burners not coming on at...
Sounds like either the flame sensor is not working.
The sequence for starting the furnace is:
1. extraction fan on
2. pressure sensor (for fan)
3. ignitor (spark or glow plug) comes on
4. gas valve opens up
5. ignition of flame
6. flame sensor (or temperature sensor)
7. plenum temp. sensor
8. main fan starts
It is most likely that the flame sensor is dirty or gone,
or (and I hope not), the module is gone and needs to
be replaced.
Sep 10, 2017 | Heating & Cooling
1 BURNER BLOWS OUT WHEN BLOWER FANS COMES ON
stop using the furnace now you have a hole in your heat exchanger
I have experienced this recently you have a lifetime warranty on that
unit .but DO NOT CONTINUE TO USE THIS FURNACE
Apr 03, 2011 | Goodman Heating & Cooling
Have a miller furnace. and when i light the pilot, and turn on the furnace. the combustion chamber comes on. it blows out the pilot whats the issue please help no heat.
if the pilot goes out before the fan comes on then your heat exchanger is plugged . if it goes out when the fan comes on then you may have a cracked heat exchanger. it also could be dirty burners with a delay. is there nd slight poping on igintion see if cross overs on the burners are dirty
Nov 25, 2010 | Heating & Cooling
Rheem 90+ NG Furnace. When furnace starts, draft inducer starts, ignitor glows and gas ignites. Burners stay lit for 10 seconds or so, then the flame reduces for a few seconds then goes out. Main blower...
Check the draft inducer air switch ( vacuum diaphragm switch) If the switch is opening when the burner starts, you might have a blockage on air piping coming into the furnace. Also prime the condensate trap on the condensate drain from the combustion fan. Also check the gas pressure, if your gas pressure is dropping, the gas pressure switch will shut it down. If it's too high the moment it comes on could raise the pressure in the furnace dropping out the combustion fan proving switch.
Oct 29, 2010 | Electric Circuit Breaker Kit for Furnace
Can you tell me the order in which each componet of a gas furnace comes on to start the furance?
Yes there is a sequence:
0:00 Dial for fan/limit switch is at 70 deg position. Furnace is cold. I turn T-stat to 80 deg to start furnace.
1:00 Burner comes on and dial begins to move slowly up.
2:30 Dial at 140 deg and fan motor comes on. Dial never goes above 150 deg.
3:00 Burner turns off. Dial slowly moves back towards 90 deg.
4:45 Burner turns on and dial is at 110 deg.
4:50 Fan turns off with dial still at 110 deg.
5:30 Burner off. Dial at 120 deg.
6:15 Fan on. Dial at 140 deg. Burner is still off.
7:00 Burner on. Dial at 120 deg.
7:40 Burner off. Dial still at 120 deg.
8:30 Fan off with dial at 110 deg., and it quickly snaps back to the 80 deg. position.
8:30 plus, cycle continues.....
Mar 25, 2010 | Heating & Cooling
Goodman GS9 propane furnace inducer motor runs continuously
it sounds like the low temp limit switch, the one that cools the furnace down with the burner off and the thermostat open, when it cools to a point the fan stops, the other switch in burner area turns burner off/on, hope this helps
Jan 31, 2010 | Goodman GMS90703BXA Heater
Furnace pilot problem
check the pilot gas pressure, might be too weak and blowing out when the blower starts, the clicking noise is the gas valve shutting down when it detecks no pilot flame, that park is normal.
Jan 10, 2009 | Honeywell Power Humidifier: Furnace...
Burners come on and go out amana 80sse
Ths is an easy problen to solve. Looking close to the burners is a pilot sensor. It looks like a thin metal pin about 1" 1/2 long. Clean this with sandpaper. This will allow you furnace to stay lit.
Hope this helps,
RepairUSA
Nov 25, 2007 | Heating & Cooling
Heating & Cooling Logo
49 people viewed this question
Top Coleman Heating & Cooling Experts
Bill Long
Paul Carew
Dan Webster
Dan Webster
Are you a Coleman Heating and Cooling Expert? Answer questions, earn points and help others