Question about Goodman Heating & Cooling
My furnace fires up and runs for about 30 seconds,, then the gas shuts off
  • 1 more comment
  • pigeonflier Sep 18, 2008
    No pilot light,, the furnace fires,, then after the blower kicks on it will run for about 30 seconds,, the the flame cuts off
  • pigeonflier Sep 19, 2008
    Yes,, it has the glow ignition,, no spark..
  • TexNOz May 11, 2010
    The flame proving sensor has failed. Just to clarify, this unit does not have a pilot light, right?
    Problem Solver:
  • 15 Answers
First we need to understand what is probably happening by understanding how this unit works.
A flame safety senses a flame and if one is not present it shuts off the gas supply. This safety is incorporated to make sure that if the flame goes out for any reason, it doesn't continue to dump gas into the furnace. Because I have no idea what type of sensors this unit uses, can you explain to me what kind of ignitor it has? See if it has a spark, or a hot surface ignitor. The hot surface ignitor will glow very bright white but looks like it's made of ceramic.
Posted on Sep 19, 2008
  • TexNOz Sep 19, 2008
    Replace the part that glows and it should work fine.
  • ash_moe_99
    ash_moe_99 Dec 31, 2012
    no it needs flame sensor sanded or change air filter it getting to hot
Amana 90 furnace won't ignite. Inducer fan runs for 30 seconds then shuts off and nothing happens. Try to turn fan on at thermostat and nothing happens. Ac works fine.
Most likely one of two issues is occurring. Either the inducer fan is not providing enough draft because it is either spinning too slowly or the impeller is damaged, or the pressure switch that the inducer motor air flow is supposed to activate is not operating properly. If the pressure switch fails to activate, the furnace will not open the gas valve and fire the ignition believing that there is not sufficient draft the vent the combustion gases.
Oct 17, 2015 | Amana Heating & Cooling
Heil nulk075dg05
You have a dirty or bad heat sensor. When you remove the front panel on you furnace you will see a probe that is 2 or 3 inches long that is in the flame when the furnace fires up. If it doesn't detect a certain temperature within the first 30 or 40 seconds it shuts down the furnace. You can either clean the probe off with sandpaper, or purchase a new one. They aren't very expensive and are easy to replace. In my experience it is usually a build up of carbon on the sensor and a good cleaning with sandpaper and alcohol usually takes care of the problem.
Feb 04, 2014 | Heating & Cooling
I have a Ducane MPGA100B4B gas furnace. The furnace only runs for about a minute then shut off. It does this far too frequent.\r\n First the induce draft blower turned on for a few seconds to check for...
Hello, sounds like the limit switch is opening on the furnace.Usually when a furnace goes off on its high limit is becuase the airflow is being restricted making the furnace overheat. a limit switch is there to protect the furnaace from overheating, most cuases are either dirt or the blower motor not running up to speed, anything that cuts down on the airflow will cause the high limt switch to open.
Feb 24, 2011 | Heating & Cooling
My gas furnace fires but then cuts out. There is a similar post on here about this but my problem is a little diiferent. The unit kicks on, fires then shuts right down. The blower comes on and stays on....
HAD A similiar problem last week with a customer who had just installed a pool and running off of propane tank for gouse as well... he let tank go empty and started having problems ..what we ended up finding is that not only was his regulator on tank bad he needed a additional regulator to regulate the different psi pressure to the appliances... get them to check your regulator out
Jan 24, 2011 | Goodman Heating & Cooling
It does not fire at all times igniter works, I can hear the gas valve when opens, some times it fires for a minute and some times does not fire at all
Problem: Your furnace will not ignite the gas to produce heat for your home. When a furnace has a bad ignitor what I see most of the time is the following sequence of operation:
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution:You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Dec 07, 2010 | Heating & Cooling
Garage furnace (standing Pilot) pilot stops after 30 mins.
it sounds like the afc the fan control not working could be dust on the afc
Jan 10, 2010 | Dayton Gas Furnace Heater
Furnace will not keep the gas burning.
May be your flame sensor on the right hand side of the burner assembly. You will need a 1/4 inch nut driver to remove it and then take a brass brush and clean off the sensor
Dec 15, 2009 | Heating & Cooling
Furnace starts properly, then shuts down, led flashes 8 times
The first thing to look at is the flame sense rod.
Shut off power to the furnace, remove, clean sensor with steel wool or sandpaper then reinstall the sensor. Reapply power and it should run properly.
Jan 10, 2009 | Goodman GMS90703BXA Heater
Coleman furnace fan keeps turning off and on every 10 seconds...
clean your heat/flame sensor with sand paper or steal wool. If the sensor is dirty, it won't detect the heat from the flame and it shuts the gas off. Clean the soot and junk off the sensor and it should work fine. I have to clean mine every year. After spending hundreds of $$ every yr on tech calls..I figured out the problem and in 30 sec I'm up and running again.
Nov 10, 2008 | Heating & Cooling
Heating & Cooling Logo
185 people viewed this question
Top Goodman Heating & Cooling Experts
Dan Webster
Dan Webster
paulcarew
Brandon Berry
Brandon Berry
Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others