How to set dip switches in highest point for multi speed blower. Have gas furnace (amana) and heatpump(amana) both 4 ton cap. My hp keeps cycling and asume is the lack of airflow.
    Scholar:
  • 68 Answers
Yes, it could very well be the lack of air flow, how to set the dip switches, need more info on the setup or diagram or instructions, write me at wbwill@sbcglobal.net, I will try to help you
Posted on Sep 16, 2008
  • William Babbitt
    William Babbitt Nov 05, 2008
    I see the problem is still on here, are you still having issues? the heat pump cycling is expensive and hard on the unit, so if you have not resolved this, it should be soon as possible.
    Check the thermostat also.
Amana 80sse furnace fire up work for about 10 min. It goes in lockout and inducer motor stay on
Robert, that is a typical indication of the furnace cycling on its high temperature switch. Look for a dirty filter, return air blockage or any other thing that would cause air flow restriction across the heat exchanger. If nothing else is evident, possibly attempt changing the heating speed to medium low or medium high for heat to improve air flow. But if it worked with no changes prior to this problem, it has to be lack of air flow that is causing the issue.
Dec 15, 2015 | Amana GMH81405DN 140,000 BTU 80% Gas...
Goodman Model GMV950905DX-an electrical surge burned out the transformer which I replaced, also replaced the circuit board. The variable speed furnace will no longer kick into high speed and it will l
If I remember correctly, there are dip switches on that control board that can be set individually. It is possible that it is just a setup issue. The switch positions should be explained in the installation instructions. I know that some Goodman and Amana two stage furnaces can be controlled by a single stage thermostat, but the dip switches have to be set properly. If the switches are set correctly the furnace will run in low stage heat for approximately 5 minutes and if the thermostat hasn't satisfied yet, it will kick in to high stage heat. I hope this points you in the right direction!
Dec 16, 2014 | Goodman Manufacturing Goodman Gas Furnace...
I have an Amana Distinction furnace, last heating season we had an issue with a lack of air movement to the second floor. We paid for a technician to come out. His solution - boost the blower speed.
If you have a variable speed motor The black wire going to the contactor relay is highest speed.or if there is a terminal strip near the motor there will be one wire and three places to plug a wire marked H, M, Low
Nov 07, 2014 | Amana Distinctions 95% Gas Furnace...
Is there an on-off switch on the furnace?
Generally, if there is not a breaker within line of sight, there will be a toggle single pole switch that will shut the furnace off. The blower cabinet will also have a door switch.
Oct 19, 2013 | Amana AMH95 - 115,000 BTU - Gas-Fired...
Amana Distinctions 5 ton premium R410A system inducer draft motor short cycling and fan does not run
Amana distinctions furnace is the top quality furnace and I would you recommend to get professional technician help for that. You may call in Toronto at 905 201-1293, Clean Air Heat is there to help you out.
Jan 01, 2013 | Amana Distinctions 95% Gas Furnace...
Payne air handler with possible GE X13 Failure
Check your dip switch settings on tonnage and your CFM per ton settings. Also make sure they wired the the low voltage for cooling to Y and not YLO if its a single stage compressor system.
Sep 23, 2012 | GE Carrier Bryant Payne 1/2 Hp 115 230v...
I put in a 90,000 btu furnace with a 4 ton blower and a 2 ton air conditioner. how can i adjust the blower speed to match the 2 ton usage
I would suggest getting a 4 ton AC. Equipment that is not matched properly usually does not function properly. What is the size of the space you are trying to cool....in square feet? One other possibility would be to try to rewire it. If it is a multispeed motor you could try to wire it to run on low speed during the AC cycle....but that's a long shot.
Sep 20, 2009 | Heating & Cooling
Trane XL19i 8? ton heat pump not heating very well
Your second stage heat check the dip switches on the board and the wires to the proper two stage heat t-stat.
Feb 06, 2009 | Omega Trane Furnace Draft Inducer Blower...
Disconnecting green wire from thermostate did allow furnace to run properly but every time I want to switch back to heatpump I must reconnect green wire again.Here is how wires are connected to...
Try this.
A T-stat.
Orange = O
Red = R (with existing jumper)
Black = C
Yellow = Y
White =W1 (Or AUG)
Green =G
At airhandler/furnace.
Green = blower wire (usually green, double check with schematic)
(Green should not go to the HP.)
Orange to HP
Red to red and to HP
black to blue (or C) and to HP
White to W
Yellow to HP. (It may also go to a "float switch" if installed. but that will just be a safety switch on the drain pan in case the line clogs and it overflows.)
The green is typically used for the blower motor. (furnace only)
The orange is used for the reversing valve. (changes from AC to heat, is located in the HP only)
Blue is typically used for common (or "C") but they may have changed it to black due to a broken wire, or other problems.
The only wires going to the HP should be
Red
Blue/black
orange
yellow
Orange should not be going to the furnace at all.
HP wiring should be
Orange to orange or O
Red to R or red