I purchase a 352AAV036060FBSA furnace. The furnace was converted to propane and is used to heat our cottage, that is only occasionally used in the winter I maintain the cottage at 10 - 12 deg.c when we are not there. In the instructions with the furnace, they recommend the lowest returna air temperature to be 18 deg.c Will I have a problem dropping this to 10 - 12 deg.c to save on feul costs when not being used Thanks Dave Zinger
Accurate Joe
  • 61 Answers
SOURCE: honeywell propane furnace. Ran out
You will need to cut off power
find the gas shut off at your unit and cut off.
Loosen the fitting after the cut off and open the cut off slowly until you smell gas. re tighten and turn gas and power back on.
Posted on Nov 29, 2008
bobicehouse
  • 1524 Answers
SOURCE: Intertherm model MGHA-090-AAPQ -- combustion air keeps running
Sounds like a problem with the circuit board.
Posted on Apr 23, 2009
  • 233 Answers
SOURCE: air conditioning runs all the time
I assume this is a manufactured home, this is probably a two transformer system, either your contactor is welded in the on positon or wyou have control wiring issues, (could be the thermostat)
Posted on Jul 12, 2009
koolbreezes
  • 540 Answers
SOURCE: furnace not blowing hot air
Also did you check to see if you added a jumper wire to the thermostat rc--rh ! R-means power to C-(cool)_--- r-power-to rh is( heat)! TYVM!
Posted on Dec 08, 2009
FurnaceGuy
  • 74 Answers
SOURCE: Central heat does not blow hot air, just warm air weakly
Sounds like some of the elements are not working. You being in Florida they may not have put very many elements in. It was 61 degrees last week. I know because I'm a Dolphin Fan. You will need a current sensing meter to check the elements.
Posted on Jan 04, 2010
Testimonial: "Perfect... The problem was with the Defrost control unit... apparently the outdoor unit was icing up every night, defrost control element was bad!"
How do I reset the temp my heat pump switches from electric to gas. It runs much more economically on electri than on propane. The thermostat is a Honeywell th8000. Code 350 setting I believe. Thanks
Heatpumps are more complex than an AC unit. Yes, there is a difference between a heatpump and an air conditioner. Where the real difference lies is out side in the condenser unit. There's a defrost board out in the unit, and depending on the brand and model, one of the wires will need to be changed so that the gas furnace will not come on. The problem with this, heatpumps use the heat that is available from the outdoors and transfers it to indoor. When the temps outside drop below 50 degrees, there's not enough latent heat to transfer, thus calling the propane furnace to operate. Without the addition of the furnace, you will not be able to heat the area properly. The only way to remedy this, is to remove the propane furnace and replace it with an electric airhandler with a heat strip for "emergency heat". The emergency heat term is used when the temps drop below the temps I mentioned above and calls for the heat strips to come on.
Feb 03, 2017 | Honeywell Heating & Cooling
Can I convert from natural gas to propane
Yes... you just need a retrofit kit.
Jan 26, 2016 | Heating & Cooling
I had a natural gas furnace installed in place of a propane gas furnace. will this cause my rollout switch to trip constantly. my fuel source is propane. gas valve on furnace wasn't change to propane
If it has a position for natural gas/propane then it needs to be changed to the position that the gas source is either propane or natural gas..
Nov 22, 2015 | Heating & Cooling
When i turn the heat up sometimes it takes a long time for the gas furnace to start ..why?
Watch your furnace when you turn the thermostat up...make sure to record everything that it is doing. If you have an induced draft, forced air system, then the heat sequence of order should go like this... Initial call for heat from tstat, Inducer vent motor turns on-pulls in the pressure switch, circuit board sends power to igniter whether it is spark or hot surface, then gas valve opens. Flame sensor senses flame, burner stays on, and blower motor kicks in to heat the space. If you notice any variance from this, then something needs to be checked by an HVAC Service Tech.
Dec 14, 2013 | Honeywell Programmable Thermostat Heater
I HAVE A 1999 GOODMAN GMT070-3B FURNACE I PURCHASED USED MUST CONVERT TO PROPANE ,BUT I CANNOT FIND ORIFICE LOCATION
it will be in the combustion chamber on the burner bar you will have to remove the burner to get to it .
Sep 04, 2012 | Goodman GMS90703BXA Heater
Can I convert a propane furnace to electric?
Actually yes! You can install electric elements in the plenum that turn on by your thermostat. The convection blower from the furnace can be used. You can also install a heat pump system that will give you both heat and air conditioning.
Feb 10, 2010 | Heating & Cooling
I want to convert a model 3e476b propane counter
The Dayton brand belongs to WWGrainger if the parts are available that would be the only place.
Oct 02, 2009 | Dayton Gas Furnace Heater
I have a dayton furnace model 3e368a serial c8425580 wondering if it can be converted to propane?
yes it can you must change the gas valve and the converter to propane,may have to change orafice on burners.any good plumber can do this for you.
Jul 11, 2009 | Dayton Gas Furnace Heater
Trouble shooting Hayward pool furnace
Big enough propane tank? proper pressure reducing valve on the propane? Check both of those.
May 30, 2009 | Hayward H Series Pool & Spa Heater 400k...
I received a Gas heating system from my dad and would like to know if I can switch it from Natural to propane gas. my model # RFN28TA.
Most furnaces come from the factory set for natural gas. If you contact the manufacturer to find the local distributor for that particular unit . you should be able to order a propane conversion kit. The kits are very easy for a trained heating guy to convert. A good handy man should be cable to do this changeover. BUT the manometer that is needed to properly calibrate the gas valve is not worth the purchase price for one application. I recommend that you use a trained heating guy.