The power overload warning should only come on if you have too much of a load plugged into the UPS. You may be close enough to the edge of the limit so the disturbance from a surge can be enough to trip the overload detector.
Your UPS is rated for 1200 Volt-Amps, so it can drive a maximum of 10 Amps at 120 Volts. Every piece of equipment should have a label with the maximum Amps or Watts on it. Add up the Amps used by the equipment plugged into the UPS/AVR sockets to make sure the total is less than 10 Amps. If the equipment label rates power requirement in Watts, divide that number by 120 Volts to get the amperage. One thing to read carefully is the label on the computer power supply. It is commonly rated in output watts, but that is not the number to use for this calculation. Since it is not 100% efficient, you need to look for the input Amps number.
If you are too close to the limit, move the printer or monitor to a surge-only outlet or consider replacing the monitor with a more energy-efficient unit. If your load total is less than 9.5 Amps, the UPS may have a defect in the power overload detection or internal voltage regulation circuits.
Only data sensitive equipment such as a computer, monitor and external drive should be plugged into these outlets.
provided in case of a power outage. Power (AC or battery) is not supplied to these outlets when the UPS is switched off. (Do not plug surge protectors or power strips into the battery back up outlets). Caution: Never connect a laser printer or scanner to the backup outlets of UPS with other computer equipment. A laser printer or scanner draws significantly more power when in use than when idle. This may overload the UPS. To Conduct a Self Test Use the self-test to verify both the operation of the UPS and the condition of the battery. In normal utility power, push the On/Off/Test button less than 2 seconds and the UPS performs a self-test function. During the self-test, the UPS operates in back-up mode. Note! During the self-test, the UPS briefly operates on- battery backup power (the on-battery LED comes on). If the UPS passes the self -test, it returns to on-line operation. If the UPS fails the self-test, it immediately returns to on-line operation and lights the replace battery LED. The loads are not affected. Recharge the battery overnight and perform the self- test again. If the replace battery LED is still on, the battery will need to replaced. This should resolve the issue for you. If you need any further assistance on the issue, you can mail me at [email protected] . I'll be glad to help you. Bye.
And caused the UPS to shutdown whenever there is Power Surge
To isolate the issue further, let me tell you the way where you can test the UPS if it is fine or not.
1. Charge the UPS for around 4 hours, and try below steps.