Question about Honeywell Heating & Cooling
Adjusting honeywell 24v gas pilot vavle - Honeywell Heating & Cooling
Need this part hard to find gas vavle made by honeywell
part#VR8205M2823
Posted on Oct 20, 2009
8" yellow flame shooting out of ignition tube when running. No adjustments that I can see on the (Honeywell) gas cut off/pilot valve.
yellow flame is an indication of incorrect air mixture
as it is gas I would suggest that you seek the services of an accredited gas specialists to do any adjustments or repairs
Nov 06, 2015 | Heating & Cooling
Smart gas valve get 24v. but pilot will not spark or light
Do you have 24 volts at the gas valve terminals when the pressure switch closes?
Dec 17, 2013 | Honeywell Furnace Gas Valve Sv9501h2409
Honeywell sv9520
check for gas at pilot tube first . if there and pilot not lighting then pilot line or orifice is clogged. if pilot is lighting check for 24v to main gas valve terminals. if have voltage either you have a bad gas valve or carry over tube on rack is clogged . if older unit clean carry over tube reinstall and check for voltage and if lights if not then gas valve is bad
Oct 24, 2013 | Heating & Cooling
I have an Americdan Water Heater 50 gal. gas. 38000BTU the pilot light does not stay lit. what can i do?
Usual problems are:. Bad thermocouple, Bad vent, blowing pilot outl. Too small of pilot flame. Low gas pressure Leaking water heater, dripping on pilot. Bad gas valve. If your water heater is more than 8 years old and the gas valve is bad, I would replace the water heater. IF you decide to replace the pilot or the gas vavle, be sure to mount pilot exactly as is was designed. If you replace gas valve get an exact replacment or a "listed" replacement. If you'rd doing this and it's older, replace the temperature/relief vavle also. Water heaters can be very dangeroius if not properly repaired/maintained.
Jul 11, 2010 | Water Heaters
Pitco frialator (propane)
Better check the incoming gas pressure first, it should match the requirement as stated on the nameplate. Low gas pressure will make the pilot flame small until it could not heat up the thermopile which will shut both main burner and pilot flame.
Apr 11, 2010 | Pitco Frialator SG18S Deep Fryer
Need schematics for honeywell s861ou3009
Those terminals are the power to the module. The tr should be the 24v (hot) line coming from the transformer. The tr/th is the common from the transformer and the th is the 24v line coming back from the t-stat. So tr stands for transformer. the th stands for thermostat. And the th/tr is the common.
I know you ask for schematics but I felt that I could easily explain it to you. It really isn't all that hard. In some cases the tr does not need to be hookup. if you only have two wires there than just hookup the th/tr and the th and it will work.
Nov 18, 2009 | GE Profile Spectra JGBP90 Gas Kitchen...
Replaced mercury thermostat w/Honeywell CT87K - doesn't work!
You need a specific thermostat for a Wall Furnace it is a Millivolt Thermostat and not a 24v standard thermostat....usually it will work anyway however if the powerpile (generator produces millivolts from the pilot light) is weak it may not be producing enough...or the Pilot light may be dirty and lazy...won't produce enough millivolts ...or you can have bad or dirty contacts or connections....or a combination of any of the above.....a 24v Thermostat and particularly a non-mercury thermostat has too much resistance in it for a millivolt system....as your Wall Furnace (other than the fan) runs on less than 1 volt
Oct 31, 2009 | Honeywell CT87B ROUND HEATING&COOLING...
Gas vavles is letting propane gas through the gas control vavle.
If you have propane you better not mess around! with nat gas its lighter than air and drafts or flies away if it can.
not so with propane , its heavier than air and stays down low!! and the most explosive situation is 10% gas/ 90% air !!!! so a small leak??? there is no such thing with propane!! turn off all valves to it and get it fixed by expert this is one repair a handyman should never do!!
Aug 23, 2009 | Cozy Enclosed Front Console Heater 20,000...
Wall heater does not work!
it sounds like the gas valve is not getting power. There is probably a saftey device that has tripped, preventing the voltage (24v) from energizing the gas valve. check for 24v throughout the circuit. It should be a simple series circuit.
Nov 11, 2008 | Honeywell Power Humidifier: Furnace...
My Honeywell gas furnace won't fire up. The pilot is working , the fan will turn on if set to manual, but won't fire. I live in Canada and am freezing. thanks.
is this a power vented system if so check the ventr motor . it must run first alowing the gravity swtch to make and send 24v to the gas valve- if its not a vented unit sounds likely you have a main valy or posibly a mercury or thermo couple problem. hope this helps.
Oct 07, 2008 | Heating & Cooling
Heating & Cooling Logo
101 people viewed this question
Top Honeywell Heating & Cooling Experts
Bill Long
Paul Carew
vance jones
Are you a Honeywell Heating and Cooling Expert? Answer questions, earn points and help others