Tip & How-To about Heating & Cooling
Charging an air conditioner by superheat or subcooling
Charging AC by superheat and subcool
First charging a unit by superheat, this is only for Acs with an orifice or capillary tube.
Optimum superheat is 12° to 15° at the compressor or suction line outside the unit.
Hook up your gages and put a thermometer on suction line (large line), start the AC. Measure the temperature of the suction line and read the pressure on your gages. Theres a temperature scale on your gages for R-22 or R-410A the needle will show you the pressure on the outer scale and if you follow it down to the R-22 or R-410a inner scale that is the saturation temperature for that refrigerant, (you can also use a temperature pressure chart), now read the thermometer, let’s say the suction temperature( the thermometer) is 67° and the saturation temperature (the gages or temp. press. Chart), is 55°, subtract the saturation temperature from the suction temperature, 67°- 55° = 12° superheat.
Charging by Subcooling, this is for Acs with a thermostatic expansion valve, it’s common to see a sight glass on the liquid line (on these units with a sight glass just clear it, when, indoor room is at approximate set point of the thermostat). If there is no sight glass then the Optimum sub cooling is 12° to 15° at the outdoor unit.
Hook up your gages and put a thermometer on liquid line (small line), start the AC. Measure the temperature of the liquid line and read the pressure on your gages. Theres a temperature scale on your gages for R-22 or R-410A the needle will show you the pressure on the outer scale and if you follow it down to the R-22 or R-410a inner scale that is the saturation temperature for that refrigerant,(you can also use a temperature pressure chart), now read the thermometer, let’s say the liquid temperature( the thermometer) is 100° and the saturation temperature (the gages or temp. press. Chart), is 114°, subtract the liquid temperature from the saturation temperature, 114°- 100° = 14° subcool.
This is also the only way to know if your a/c has the proper charge.
Heating & Cooling Logo
Charging chart missing. Goodman 4-ton AC (model CK 49-18) What are the high and low suction pressures at 90 degrees F?
Hello, if this is a R-22 unit your low side should between 70-75 psig and high side should be between 225-230psig. But keep in mind always measure the superheat if it is a fixed orifice and subcooling if it is a txv unit
Jun 07, 2011 | Amana Heating & Cooling
i have a 4 ton outside and a 5 ton coil inside square footage of the house is 2495 living.my preasures are 75 low side and 225 hi side i'm not getting any flood back is this ok are do i need to add more freon
Charging by Subcooling, this is for Acs with a thermostatic expansion valve, it’s common to see a sight glass on the liquid line (on these units with a sight glass just clear it, when, indoor room is at approximate set point of the thermostat). Optimum sub cooling is 12° to 15° at the outdoor unit.
Aug 09, 2010 | Amana Heating & Cooling
How to refill gas in home spli a/c, advise presure details as wel
Mar 19, 2010 | Panasonic CW-1006FU Air Conditioner
gas pressure
It depends on the indoor and outdoor temperature and humidity. The low side pressure can be in the area of 135# to 145# with an indoor temperature of 80° and 50% relative humidity, and the outdoor pressure can be in the area of 300# to 330# on a 95° day depending on effeciency rating.
If your asking this to charge your a/c this is not how to charge your a/c.
Dec 25, 2009 | Heating & Cooling
when i was fixed a problem in central ac trane i found decreased in freon r22 and the suctione line was freezed, i charged the ac with froen gas r 22 then i found that the suctione line changed and begin to melt the ice so a few minutes and the suctione became not cold and there wasnt enough cold air in the room and the low pressure gage increased 10 bar psi so what is that.?????????
You are still low on freon. Charging AC by superheat and subcool