Tip & How-To about Carrier XHB123D X/Y Series Heat/Cool Air Conditioner
Why your unit is freezing up.
To understand why your AC or heat pump is freezing up, it helps to know how your system works.
There are 7 major parts to an AC system, 9 with a heat pump.
1 - Condenser/heat pump (The outdoor unit)
2 - Air Handler (the indoor unit unless the system is a package unit, then all is outside in one system. The air handler is usually found under the home, in an attic, or in a closet.)
In the condenser are the following major parts.
3 - Compressor
4 - Condenser coil
5 - Condenser fan
6 - (HPs only) reversing valve
In the air handler are the following major parts.
7 - Blower motor
8 - Evaporator coil
9 - (HPs only) electric heat strips
Some systems known as "dual fuel systems" use another heat source in place of the heat strips, usually a gas furnace. I will address gas furnaces in another post.
When an air conditioner is operating properly several things are taking place.
1 - The compressor is compressing or "pumping" refrigerant through the system.
2 - through changes in pressure, the refrigerant makes the evaporator coil get very cold, and the condenser coil gets very hot.
3 - The blower motor/fan circulates air across the evaporator coils, as the room temperature air (Also known as "indoor ambient") goes through the cold coil, it exits, cooled approximately 15 to 20 degrees cooler than when it entered. (In a ducted system, the blower is also the fan that circulates the air throughout the home.)
4 - The condenser fan circulates air across the condenser coils. As the outdoor air goes through the condenser coil, it removes heat from the coils that are very hot. This in turn removes heat from the refrigerant so it can run its cycle again, and through pressure changes, cool the evap coil.
5 - With a heat pump, the reversing valve reverses the flow of refrigerant in the condenser and evaporator coils.
In AC mode, the evaporator coils get cold, and the condenser coils get hot. But in heat mode, the evaporator gets very hot, and the condenser very cold.
Now, whichever coil is getting cold will freeze up if there is inadequate air flow across the coil, as the refrigerant in it is far below freezing, and there is not enough airflow to keep the humidity in the air from freezing on the coil.
Things that can cause poor airflow are,
1 - Dirty/clogged coils
2 - dirty/clogged filter (will only effect evaporator coil)
3 - Closed/blocked vents (will only effect evaporator coil)
4 - Malfunctioning or dirty fan
Low refrigerant will also cause a coil to freeze up, reduce efficiency and cause the system to run for long periods of time. Not to mention, shortening the life of the unit.
With a heat pump, in heat mode only, the condenser (outdoor) coil will routinely begin to freeze up in cold temperatures. This is due to the fact that the refrigerant is below freezing, and the cold outdoor ambient temp is not warm enough to keep the condensation in the air from freezing on the coil.
Note, a properly working AC should never freeze up.
A heat pump is equipped with defrost controls to prevent ice buildup.
Some are controlled by timers, some by temp.
When a HP is going into defrost mode, the condenser fan shuts down, the reversing valve reverses the flow of refrigerant and the once cold condenser coil now gets very hot, defrosting the coil. (Many people have said this process sounds like the unit is coming apart, or about to explode and are frightened by the "smoke" which is really just steam from melting ice that comes off the unit.)
During defrost mode, the secondary or "auxiliary" heat comes on to ensure that you are still getting warm air from the vents. (Again, this can be electric heat strips or a dual fuel system)
If you are experiencing cold air from the vents during defrost, that means your auxiliary heat is malfunctioning.
The auxiliary heat is used for three purposes.
1 - during defrost mode to maintain warm airflow (automatic)
2 - when the HP cannot maintain the set temp due to extreme outdoor temps. It comes on when the indoor temp drops several degrees below the set temp on the thermostat (automatic)
3 - For emergency heat source when the HP is not working. (Manual)
To recap....
Iced up coils?
Poor airflow
low refrigerant
Malfunctioning fan
failing defrost system
There are two things that can be done in a pinch to help de-ice frozen coils. This may get you by until the repairman can get there, or you can fix the system if you are a do-it-yourselfer.
HPs frozen outdoor coil in heat mode, not going into defrost?
Cover most of the vents, and turn the system onto cooling mode until the outdoor coil is thawed. then uncover vents and return to heat, or emergency heat. (this usually takes 15 min or less)
Frozen coils in AC mode with a heat pump?
Turn the system to heat with the thermostat on just high enough to get the system to come on. (again, usually takes 15 min or less to thaw.)
AC only, with frozen evap coils? (this can sometimes be seen frozen all the way outside to the compressor on the copper lines.)
Turn the system off, and the fan switch from "auto" to on".
This will usually defrost the coils within 1 to 2 hours.
(If your system has the furnace in line before the evap coil, turn the system to heat, and the furnace will defrost the coil within minutes.)
Carrier XHB123D X/Y Series Heat/Cool Air Conditioner Logo
I NEED TO REPLACE MY AIR COMPRESSOR OR CONDENSER I DON'T KNOW WHICH ITS CALLED ON MY 2000 PONTIAC SUNFIRE
The condenser sets just behind the radiator in your car. It is the high pressure, high temperature coil for the air conditioning system in your car. You cannot just install a new condenser and fill the system with refrigerant. You absolutely must evacuate the AC system using a vacuum pump first. This removes any water vapor that is in the AC system. This water vapor will freeze and thaw in the AC system, which will cause major problems in cooling performance.
Aug 08, 2015 | 2000 Pontiac Sunfire
2001 cadillac dts no heat at idle car starts to run hot
Maybe the water pump has been eaten away
The GM Dexcool hasn't worked out well for the last
years or so
May have to do the water pump & go to a universal
coolant
If your saying it is only a cabin heat issue then your going
to have to understand the system & diagnose that part
Mar 03, 2013 | 2001 Cadillac DeVille
put on a new thermostat.......added a 5 wire to the system and does not work now
dont understand what you are trying to say. What is name and model of unit. what is name and model of the thermostat. do you have straight ac with gas heat, straight ac with electric heat, heat pump, heat pump with back up heat and what kind, electric or gas?
Jul 07, 2011 | Heating & Cooling
My 1999 V70's AC stops working after a few minutes
this is a major problem on 850 and s-70 models with ECC climate control these cars have MAJOR problems with this system and you MUST have major knowledge of system to diagnose and fix
Jun 08, 2009 | 1999 Volvo V70
curtailment active
A follow-up to my previous post. I talked with a technician from the Co that installed my unit, and the issue lies in the "Utility saver mode" for the 2 stage heat pumps, and having the high stage locked out. In the Advanced Setup menu (hold the "Advanced" button for 10 seconds to access this menu, look for the "Utility Saver" menu item. Select it and your system probably shows that "Utility Saver" is enabled, which only allows your heat pump to run on the low stage and not the high stage. If you change the the setting to be disabled, this will allow your system to run at the high stage and should solve your problem.
I have not changed the settings on my system yet to confirm this solution. That will have to wait until I get home this evening.
May 11, 2008 | Carrier XHB123D X/Y Series Heat/Cool Air...
13,281 people viewed this tip
Top Carrier Heating & Cooling Experts
Dan Webster
Dan Webster
Bill Long
Are you a Carrier Heating and Cooling Expert? Answer questions, earn points and help others