20 Most Recent
Soleus KFR-24G Air Conditioner Questions & Answers
I have a Soleus Air
You most likely have a bad capacitor, contactor, thermostat problem or the outside unit is not getting the 220 VAC power that it requires. Follow the following procedure to diagnose your a/c system ONLY if you are comfortable enough with your competency in working with high voltage devices.
***CAUTION***
Anytimeyou are working on or around electricity you run the risk of shock and ordeath. If you are not competent working with high voltage and using electricaltest equipment then please consider consulting an expert before you open anelectrical panel or appliance. You assume any and all liability by continuing withthis diagnoses process.
Typical Contactor
Full d image
Thecontactor pulls in to make contact between L1 to T1 and L2 to T2, L1 and L2 arethe main power coming in to the unit and T1 and T2 are the loads I.E. thecompressor and fan motor. Use a multimeter set to AC Volts and test the powercoming into the unit by placing one probe on L1 and the other probe on L2 andread the number that the meter reads. If it is between 208 and 240ish then theunit has the proper power to operate and we must go further to diagnose theproblem.
Next, use ascrewdriver with an insulated handle to press the "button" in themiddle of the contactor, the one labeled "Pulls in with 24VAC", ifthe unit starts and runs while you are pressing this in then the contactor isnot pulling in and either is not getting the 24 volts AC from the thermostat oris bad and needs to be replaced. If the unit does not run then we continue withthe diagnoses by testing the capacitor.
***CAUTION***
Capacitorshold a large electrical charge and will discharge upon contact with your skin.This is enough to stop your heart and cause death. If you are not confident ofyour abilities around these devices then please leave any testing or repairs toa professional.
The capacitor is inside the unitand you have to remove the cover to see the inside of the electricalcompartment. You will need to discharge the capacitor before you start workingaround it. To do this take a screwdriver or other long metal tool with aninsulated handle and cross the three terminals on the capacitor to ground. Youthen remove the wires to the capacitor terminals, taking note of which wiregoes to which terminal.
Capacitors are rated in MicroFarads (marked by a µF symbol) and a dual capacitor, shown in the image below,will have two ratings listed like this "35/5µF" or something verysimilar. You must have a multimeter thatreads micro farads " µF " to check a capacitor.
You do that by placing one probeon the C or COM terminal and the other probe on the FAN terminal and it shouldread the small number of the rating, for example if your capacitor is ratedlike this: 30/7.5µF then the fan rating will be the smaller of the two numbers.In this case the 7.5µF (seven and a halfMicro Farads). The HERM terminal is the one for the compressor and will berated the higher of the two numbers, I.E. the 30µF on the capacitor. Check themboth and of they are more than 6% lower than they are supposed to be then thecapacitor is weak and needs replaced. If you read 0 (zero) then the capacitoris bad and needs replaced. If they are within 6% of rated capacity then thecapacitor is OK and we move on to the next component.
Typical Dual Capacitor
Fulld image
Next we testto see if the thermostat is sending the "signal" to the contactor topull in and supply the power to the compressor and fan motor. The thermostattakes the 24 VAC, that's 24 Volts AC, from the transformer in your furnace/airhandler and sends it to the proper place depending on if you have it set forheating or cooling. Think of the thermostat as a switch, this switch sends the24 VAC to whatever units needs to come on at that particular time, whether it'sheating or cooling.
During acall for cooling the thermostat (T-stat) sends the 24 VAC to the contactor inthe outside condensing unit and turns it on. We need to find out if this signalis getting to the contactor or not so we can determine if the contactor is bador the problem lies elsewhere. Do this by setting your multimeter to AC Voltsagain and placing the red probe to the side of the contactor where the 24VACwires connect and the black probe to the metal casing where it can get a goodground. Read the meter and if it reads 24 volts or more, up to 27 or so, thenthe signal is getting through but the contactor is not operating and we need toreplace the contactor.
If we do nothave the proper signal there then the contactor is most likely OK and we needto look at the t-stat and the t-stat wiring. Check the batteries in your t-statand see if that helps. If your blower motor in your home at your furnace/airhandler comes on when you set the t-stat to cool then we know that the t-statand the transformer in your furnace are both operating and you need to checkfor breaks in your t-stat wiring from the t-stat to your furnace and then fromthe furnace to the outside condensing unit and repair as needed.
Hope thishelps and remember, safety first and if in doubt call a professional.
Need Replacement filters for Soleus R150
If you need replacement filters for your Soleus R150 air purifier, you can try the following steps:
- Check the user manual: The user manual for your Soleus R150 air purifier should provide information on which type of replacement filters are compatible with your device. Check the manual to find out which filters you need to purchase.
- Contact the manufacturer: Reach out to the manufacturer of the air purifier to inquire about replacement filters. They may be able to provide you with the filters you need or direct you to a retailer that carries them.
- Check online retailers: Many online retailers sell replacement filters for air purifiers, including Amazon, Walmart, and Best Buy. Check these retailers to see if they carry the filters you need.
- Visit a local retailer: You may be able to find replacement filters for your Soleus R150 air purifier at a local home goods store or home improvement store. Check these retailers to see if they carry the filters you need.
When purchasing replacement filters for your air purifier, be sure to check that they are compatible with your specific model of air purifier. It is also important to follow the manufacturer's instructions for replacing the filters to ensure that they are installed correctly and functioning properly.
E4 error on my soleus air conditioner model lx 1400
E4 Outdoor activation of low pressure switch/ less suction pressure.
Check back pressure, which should be 60 PSI when ambient temp 98 degree.If not Short of gas- find leak and arrest. And do gas charging. Even due to indoor coil dust blocked also e4 arise. Clean the coil and reset it