20 Most Recent
Square D Ehb24020pl 20 A Ehb4 Ehb Circuit Breaker Questions & Answers
How does a 208V 24Coil Relay works?
A 208 volt 24 volt coil relay is rated for use at 208 volts at the relay contacts. The coil used to energize or closed the relay contacts are operated o 24 volts .a 24 volt transformer is used for the coil circuit.
Hope this helps.
Bob
12/17/2014 3:49:25 AM •
Square D...
Answered
on Dec 17, 2014
I installed a 3 ph 208v Square D starter with 2-
1. Why not buy a phase loss monitor that monitors all 3 legs. 208v 3ph is 115-120V to neutral. If you're using two 120V relays you'd only be monitoring 2 legs of the 3 phase. Using relays can be risky, as sometimes when you loose one phase you'll still pick up voltage through your load. If your set on using relays use 2-208V relays. Connect one to phase A+B and the other to B+A and then wire two of the normally open contacts in series and put that in your circuit with your pressure switch. I'f you're using 208V for control voltage, then you need to take L2 to the oveloads and then to the coil. L1 would go to your pressure switch, and the return from the pressure switch would go to the other side of your coil. You could add your phase loss protection here.
7/24/2010 2:54:56 AM •
Square D...
Answered
on Jul 24, 2010
Ehyb4 circuit breakers
First switch off the power at the main breaker or pull the meter from the meter socket. If you flip off the main breaker and it is mounted in the same breaker panel, just be aware that the wires above the breaker are still hot. Connect the white wire to the neutral bar, the green wire to the ground bar, and the black wire to the breaker. Then tilt the breaker to get the front black lug under the bar and push the back of the breaker onto the lug on the bus bar.
6/30/2010 11:47:06 PM •
Square D...
Answered
on Jun 30, 2010
High amp start up draw
I don't care what kind of stories Craftsman tells, their numbers don't add up.
One horsepower is ~ = 740 watts of energy.
2.5 hp equates to a steady-state power consumption of ~1850W and this could be 50% higher during the first second or two after turn-on.
Your 15 Amp circuit is pushed to the limit by that power level; 15 Amps X 120 VAC = 1800W
And, motors aren't a breakeven game; part of the power they draw is wasted in heat.
9 amps steady-state would be a power consumption of over 6kw which cannot be right.
Either your measurements or the motor is faulty.
10/8/2009 11:04:29 PM •
Square D...
Answered
on Oct 08, 2009
Square D circuit breaker in a home fuse panel and I have already replaced the breaker with a new one.
i strongly recommend that you get in an electrician to investigate the problem
from your description of the amount of power required from your circuit breaker I would consider that there are to power wires from the back of that unit
one circuit to run half the points and another wire to run the rest
If only 1/2 are working, I am thinking that one of the wires at the back of the breakers is loose or come undone/broken and that will require the services of an electrician
To further explain this line of thought, each circuit in a house is designed to carry a maxim of 10 amp total (wire current capacity) so that with all outlets in operation the maximum current is 10 amps
if the required current allowed exceeds that the electricians break the numbers up so that a second circuit is employed again up to 10 amps max
if again there was a requirement that exceeded the 20 amps ( circuit breaker amp) a second circuit breaker would be installed and a 3rd circuit and so on
3/31/2017 1:55:10 PM •
Square...
Answered
on Mar 31, 2017
On a 60 FT. run using 12/2/G wire can I use a 25amp. breaker safely?
The size of the breaker that you are going to use on a circuit is predicated on the current draw of the appliance(s) you have on the circuit. Assume you have them all turned on, add up their respective amperages and , voila, you have a close approximation of the size of the breaker. If you do not know the amperage look for watts info. Divide the latter by voltage of 115 and you will arrive at the amps used.
9/25/2015 5:02:51 PM •
Square...
Answered
on Sep 25, 2015
Electrical panel dead, main and all breakers
Then, call PG&E...or your local utility company to come out and check your meter. PG&E, or your local utility company are responsible for the power up to the meter at your electrical service panel. After that, it's the electrician's responsibility...
7/1/2014 8:18:25 AM •
Square...
Answered
on Jul 01, 2014