Will this 3 Amp Circuit Breaker 250vac/50vdc work on a heat pump control wiring ?

Will this 3 amp breaker work on a heat pump replacing the fuse and trip the breaker if a short is present in the 24 volt control wiring ? Is this breaker for ac current & dc current ? Thank You

1 Answer

Vernon Taylor

Level 3:

An expert who has achieved level 3 by getting 1000 points

Superstar:

An expert that got 20 achievements.

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

  • Heating & Co... Master 7,446 Answers
  • Posted on Nov 14, 2017
 Vernon Taylor
Heating & Co... Master
Level 3:

An expert who has achieved level 3 by getting 1000 points

Superstar:

An expert that got 20 achievements.

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

Joined: Oct 05, 2008
Answers
7446
Questions
0
Helped
1957606
Points
26207

The dc rating of switch or relay contacts is always lower than ac due to dc current, especially with an inductive load, arcing more and longer when the circuit breaks.

On some circuits a reverse diode can be fitted across the contacts to reduce arcing and on ac a small value capacitor can have a similar effect.

Most switches and breakers have ratings for ac and dc and are suitable within those ratings. Switches that are primarily designed for dc inductive loads generally have a rapid spring assisted make and break.

I think the answer to your question is yes.

Testimonial: "Thank you, I ordered a few of them and going to try them out to see how they work."

5 Related Answers

Anonymous

  • 1 Answer
  • Posted on Nov 22, 2008

SOURCE: Heat pump trips circuit breaker

i want to know the size of breaker to use.we are using a 30,30,30,30but it is kicking off.would a 40,40,40,40or higher be better if they sell them.

Ad

Anonymous

  • 10865 Answers
  • Posted on May 02, 2009

SOURCE: Pond pump trips circuit breaker

The circuit breaker trips because there is an electrical short in the pump itself or in the wire feeding the pump. A cause of this could be a bare wire, or a crack in a wire. Remove the pump and put it in a five gallon pail of water and test it. If it still trips the breaker you will know the problem is in the pump or the cord to the pump.

Anonymous

  • 1515 Answers
  • Posted on Dec 07, 2009

SOURCE: I have 60 amp circuit breaker on my electrical a/c

You're unit is a 31/2 ton according to the numbers.Normally, breakers will only be in a half way posistion when tripped. Yes, under most conditions, the fuse will blow before the breaker trips. I have seen this many times, the breaker may be weak, burned, loose wires and so tighten wires, check the condition of the breaker.It sounds like the breaker even though it is 60 amps, is the problem and you should replace it with out hesitating. This will solve you're problem. When you pull the breaker out, look at the metal clips that snap in on the buss bar to see if they have been overheating.And the buss bar its self. You will know. I am sure this will take care of you're problem. Good Luck,
Shastalaker7

Testimonial: "Thank a lot this was very helpful"

Anonymous

  • 145 Answers
  • Posted on Jan 08, 2010

SOURCE: Can't find any ite bl circuit breakers.

YOU CAN CALL ITE FOR A DEALER NEAR YOU

motor1258

Mike Butler

  • 6674 Answers
  • Posted on Jul 25, 2010

SOURCE: AC runs for 5 minutes and then circuit breaker

What else do you have running on hydro while AC is running? Such as coffee maker, microwave, water heater, fridge. That 30 amp breaker is your main breaker I assume, or breaker on pole your plugged in to. Keep in mind your AC will normally draw approx. 15-17+ amps momentarily when compressor kicks in to cool, then drop back to 12-15 amps when running normal. If your AC is drawing too much current, then you would only normally trip 20 amp breaker for AC in your panel. Try switching other appliances to gas operation while running AC, such as water heater, and fridge. Make sure incoming voltage is up to specs as well . (115-120 volts)
If water heater takes 5-8 amps, and fridge takes same when they are calling for power, you'll be close or over the 20amp mark when you consider your on board converter etc. as well. That only leaves approx 10 amps for AC that requires approx 15 amps to run, and up to 20amps when compressor kicks in. If you switch all those other items over to propane, and it still happens, then a current draw test should be done on AC unit to see if perhaps a capacitor is faulty, or possible compressor faulty.

Ad

Add Your Answer

×

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

0helpful
2answers

Keep blowing fuse for sterio which kills water pump and ac what are possible problems ?

FUSE WAREHOUSE HUH? oK, IF FUSE REPEATEDLY BLOWS, GLASS TUBE? CORRECT? tHEN YOU HAVE A SHORT CIRCUIT OR ACIRCUIT OVERLOA.D. tHE PUMP MAY BE TAKING OUT THE STEREO BECAUSEPUMPS PULL AMPS WAY MORE THAN PRETTY MUCH ANYRHING ELSE.. The pump should have a dedicated circuit. Or remove anything piggy backing on the pump circuit and bump the fuse 5 amps. Here is a trick of the trade. Go to autozone and chk out the AUTOMATIC CIRCUIT BREAKERS. bUY ONE THAT WILL FIT WHERE THE FUSE WENT.dO NOT GET THE SAME AMPERAGE. IT WILL FLUTTER LIKE A TURN SIGNAL FLASHER. NOT DESIRED BECAUSE WHILE THE BREAKER KEEPS ON AND OFFING, yOU WILL HAVE THE TIME TO REMOVE SUSPECTED WIRES. wHEN BREAKER STOPS TRIPPING, YOU HAVE FOUND THE PROBLEM CIRCUIT. tO SLOW DOW THE TRIPPING OF THE BREAKER, GET A HIGHER AMP BREAKER. bUT! dO NOT BUMP IT UP MORE THAN 5 AMPS AT A TIME OR THE RISK OF OVERHEATING YOUR WIRING SOARS. i ALWAYS HAD SOMEONE ASSIST AND WATCH FOR PROBLEMS LIKE WIRES HEATING UP, SMOKE OR SMELL. i DON'T MEAN TO SPOOK YOU, BUT YOU ARE BYPASSING THE DESIGNATED THRESHHOLD BY USING AN ALTERNATE TYPE OF CIRCUIT BREAKER WHICH RAISES THE THESHOLD IN ORDER TO DETECT AND LOCATE YOUR PROBLEM. iF THE
BREAKER CLICKS RAPIDLY, YOU HAVE A DEAD SHORTsLOW ORWIDELY SPACED TRIPPING MEANS YOU HAVE AN OVERLOAD SITUATION(TOO MUCH DEMAND ON THAT CIRCUIT. iF YOU WANT, AFTER ALL IS SAID AND DONE, TO USE AUTO CIRCUIT BREAKERS, gET THOSE OF THE SAME AMP RATING AS THE GLASS TUBE(BUSS FUSE. tO ME, THE METAL CASED ONES ARE FLAME PROOF WHERE PLASTIC MELTS .. tHEY AREN'T CHEAP BUT WORTH A TON OF BUSS FUSES. gOOD lUCK AND BE SAFE - T tHANKS FOR USING FIX-YAED NED-
0helpful
1answer

I HAVE A 2 1/2 TON PACKAGE HEAT PUMP . THE60 AMP BREAKER AT THE DISCONNECT BOX KEPT TRIPPING . I DISCONNECTED THE HEAT STRIPS AND NOW THE 60 AMP BREAKER ISNT TRIPPING . WHAT IS CAUSING MY BREAKER TO T

You need to check the current rating of your heat strips. If it is more than 60 amps then you need a bigger breaker. If 60 amps or less then your heat strips are going bad. Also make sure your fan turns smoothly without any wobble.
0helpful
1answer

No lights upstaires circuit breaker keeps tripping

Jan 2013
1) Move wire to another same-size circuit breaker to eliminate bad circuit breaker as suspect.
Do NOT increase size of breaker or it will cause fire.
http://waterheatertimer.org/How-to-replace-circuit-breaker.html
http://waterheatertimer.org/Troubleshoot-household-electricity.html

2) Put hand on each appliance and outlet to see which ones are warm. Outlet should never be warm or hot. Replace outlet. Inspect wires for loose and burned connections.

3) If the breaker is good, then add up total watts being used by checking watt rating on each device. 100 watt light bulb is 100 watts. Big screen TV has a label that shows 300 to 500 watts. Computer has label. Space heater has label showing 1500 watts. Iron has a watt rating label. Take total watts and divide by 110Volts and this will give amp load. Total watts used = 2000 and then divide 2000 by 110 volts = 18.8 amps
Compare amp load with circuit breaker.
20 amp circuit breaker has 80% safe maximum, or 16 amps.
If amp load is 18.8 amps, then 20 amp breaker is starting to get hot, and weak breaker will start tripping.
If amp load is 18.8 amps, and breaker is 15 amps, then you are overloaded and breaker is feeling the heat, and tripping because of heat.
Solution is to reduce amp load.

4) If you have short circuit, that can also trip breaker.
Unplug everything and then plug things back in slowly to see which plug or appliance is causing the problem.

If you need further help, I’m available over the phone at https://www.6ya.com/expert/gene_9f0ef4df2f9897e7

1helpful
1answer

How do i know when 220 circuit breakers are bad

Always match breaker and wire size:
http://waterheatertimer.org/Color-codewire.html
http://waterheatertimer.org/How-to-replace-circuit-breaker.html

Feel if breaker is getting warm.
Listen for crackling sound.
Breaker is tripping.
Move wires to another same-size circuit breaker and see if problem continues.

Check watt or amp load on breaker.
For example water heater label shows 4500 watt non-simultaneous.
4500 watts divided by 240 volts = 18.75 amps.
You might think 20 amp breaker was good in this case.
However electricians use 80% safe maximum.
20 amp breaker x 80% safe max = 16 amps.
Water heater is 18.75 amps, so install 30 amp breaker.
30 amp breaker uses 10 gauge wire.
This means wire to breaker will run cool and not get hot, so breaker lasts longer, and there is more efficiency.
Using 80% safe maximum rule protects home, reduces heat wear on breakers and breaker box so everything lasts longer.

If you need further help, I’m available over the phone at https://www.6ya.com/expert/gene_9f0ef4df2f9897e7

Nov 18, 2012 • Dryers
2helpful
2answers

Breaker trips after bout 5 minutes

Breakers trip because of heat.
When heat from wire exceeds breaker rating, it trips.
Something is causing heat on the wire, wire is too small for the amp draw, there is short circuit, or breaker is bad.
Replace breaker and/or test wire.

Put amp-meter on wire and read amp draw through wire.
Amps cause heat. That's why high voltage lines from power station are high-volt-low-amp so there is no heat loss with long distance transmission, until transformer at home converts electricity to lower volts and high working amps with enough power to run electrical devices.
Same is true for AC and DC circuits.
If amp reading on wire exceeds rating on breaker for length of time, then breaker will trip.
The fact that the breaker lets current (amps) to flow for a period of time before tripping is because the breaker is probably rated for slow-acting, or it takes a while for amp draw to heat the wire.

Following image shows amp-meter that clips over wire to get amp reading.
http://waterheatertimer.org/pdf/Which-is-best-gas-water-heater.pdf

If you need further help, I’m available over the phone at https://www.6ya.com/expert/gene_9f0ef4df2f9897e7

0helpful
1answer

I have a Fimco 2100 model sprayer that keeps blowing the fuse. Wiring is all ok. Pump doesn't even attempt to turn on. Fuse blows almost 1 second after pump switch is turned on. Pressure gauge never...

The breaker is too small, the cord is too small, the starter motor on that thing draws 18 amps. It will trip any 15 amp breaker and any 20 amp breaker with something else running, any cord will drop the amp below the starter winding min. make sure nothing is running, separate circuit if you can find one, no extension cord, and a 20 amp breaker in the fuse box. if that is not the problem , then something is shorting out when you hit the switch. Check the wiring on the pump and make sure all is secure, no loose wires, no sparks. My compressor won't run on any old plug, has to be 20 amp, has to be without a cord or with a heavy cord, and has to be hot out, if it is cold, forget it!. We have to keep the compressors in a heated room so they will run in the winter. Hope this helps.
Jul 08, 2011 • Garden
0helpful
1answer

When specs say circuit requirement is 40, do they mean the breaker size?

What are you wiring?
Does it seem realistic that you need 40 Amp capacity?

40 Amp circuit breaker is usually 240 Volt and it goes to heat pump, double oven, or some heavy equipment. 40 amp breaker uses 8 gauge wire.

You can figure a circuit with the formula V x A = Watt
If your VA is 7500 Watts and voltage is 240, then Amps is 31.25
2helpful
1answer

Relay Box for 1994 ford mustang cobra

relays are normally in the fuse panel on the left side of dash by knee.

Fuses and Circuit Breakers Location and Values
NOTE: The headlamp switch (11654) has an integral 20-amp circuit breaker.
  • The combination instrument panel fuse and circuit breaker panel contains most of the fuses and circuit breakers used in the system.
  • The fuses and circuit breakers are color-coded by amp rating.
  • The locations and values of the fuses and circuit breakers not contained in the panels are shown in the following chart.


Circuit Circuit Protection and Rating Location Headlamps and High Beam Indicator 20 Amp. CB Integral with Lighting Switch Heated Back Window 16 GA Fuse Link Engine Compartment Power Windows, Power Seat, Power Door Locks 20 Amp. CB Starter Motor Relay Load Circuit Fuse Link In Harness Engine Compartment Lamp Fuse Link In Harness Convertible Top 25 Amp. CB Lower Instrument Panel-Reinforcement


732ccd2.gif
Cavity Number Fuse Rating Color Circuit Protected A 40 Amp Orange
  • Ignition Switch
B 40 Amp Orange
  • Ignition Switch
C 40 Amp Orange
  • Ignition Switch
D 50 Amp Red
  • Headlamp Switch
  • Instrument Panel Fuses 4, 8 and 16
  • Instrument Panel Circuit Breaker 12
E 20 Amp Light Green
  • PCM
  • Fuel Pump
  • HO2S (3.8L)
  • Canister Purge Solenoid
  • EVR Solenoid
  • Ignition Control Module (3.8L)
  • IAC Solenoid
  • Fuel Injector
  • Automatic Transmission
  • Camshaft Position Sensor (3.8L)
  • MAF Sensor
F 40 Amp Orange
  • Heated Back Window
G 20 Amp Yellow
  • Fuel Pump
H 60 Amp Blue
  • Fan Control
J — — Not Used K 10 Amp Blue
  • Anti-Lock Brake Control Module
L 20 Amp Red
  • Fan Control Monitor (PCM)
M 25 Amp Yellow
  • Horn
  • Foglamps
  • Daytime Running Lights Control Module
N 25 Amp Clear
  • Fuses 5 and 9
P 20 Amp Clear
  • Radio Amplifier
Q 20 Amp Yellow
  • Generator
S 30 Amp Yellow
  • Convertible Top Motor
T 60 Amp —
  • ABS
Not finding what you are looking for?

154 views

Ask a Question

Usually answered in minutes!

Top Heating & Cooling Experts

Paul Carew

Level 3 Expert

3808 Answers

john h

Level 3 Expert

29494 Answers

Brad Brown

Level 3 Expert

19187 Answers

Are you a Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...